[Equest-users] Fedx
Paul Diglio
paul.diglio at sbcglobal.net
Thu Mar 3 13:11:20 PST 2011
Richard:
I would base the model on one boiler/hot water loop with heating coils in each
air handler. As far as airflow, I would let eQuest autosize the CFM. Run the
simulation and if there are excessive unmet hours that cannot be corrected by
throttling range adjustments, try bumping up the airflow above the amount that
eQuest calculated.
Fan energy is calculated using the CFM, minimum motor efficiency and estimated
duct static loss per 90.1-2007 6.5.3.1.1A.
For the VAV portion, you can set the minimum and maximum fan ratios or you can
define a discharge air reset schedule.
Paul Diglio
________________________________
From: "RJTHEACMAN at aol.com" <RJTHEACMAN at aol.com>
To: equest-users at lists.onebuilding.org
Sent: Thu, March 3, 2011 12:47:49 PM
Subject: [Equest-users] Fedx
I am modeling a 110,000 sf. Fedex sorting facility for LEED and the building
has a small office area that is heated and cooled by rooftop units and the
remainder of the warehouse is only heated.
In accordance with ASHRAE 90.1 2007 if no cooling system exists the cooling
system shall be identical to the system modeled in the baseline building
design.
That system is a system 5 packaged vav with reheat, which includes a hot water
boiler.
We have (15) gas-fired unit heaters that provide heat to the warehouse.
My question is do I set up my heating system with 15 hot water boilers, the
same heating capacity as the unit heaters?
For the fan energy, do I set my air quantity the same as my unit heaters?
How do I address the VAV portion of the system as well as the hot water pumps?
I have my model setup with (2) separate HVAC systems (1) Packaged VAV with
Reheat and (2) Packaged rooftop DX units with a gas furnace.
Any help will be greatly appreciated.
Richard Dominick, P.E.
TEC Engineers, LLC.
Norwalk, CT.