[Equest-users] Different zoning per floor
Carol Gardner
cmg750 at gmail.com
Wed Mar 9 11:12:39 PST 2011
Jamil,
I am not sure why you want to use the Schematic Design Wizard. It is quite
limited in what it can do. I think you would be better off using the Design
Development Wizard.
Charles is correct to advise you to use two separate shells and to locate
them relative to each other using the x y and z coordinates on the Wizard
Screen 1 of each shell. Be sure to check the box that says Specify Exact
Site Coordinates and set your x, y, and z to 0, 0, 0 for your first shell.
Follow the same procedure for your second shell and set the x, y, and z to
their proper values, which will usually, but not always, be 0, 0, height of
the first shell.
With regards to zoning, you can easily put in different zoning for each
shell in the Design Development Wizard. This is done on Screen 2 by setting
the Zone Pattern to Custom and creating as many zones as you want of any
shape that you want. You can also use the Detailed Design Wizard to specify
your window, wall, and door layout and to take a first crack at specifying
your constructions, internal loads, and HVAC systems. Notice I say "first
crack" for many of these items. You will want to carefully evaluate your
internal loads and schedules, constructions and HVAC system inputs that the
wizard creates to see if they match what you want in your final model.
Hope this helps!
Carol
On Sun, Mar 6, 2011 at 9:47 PM, Charles Land <cland at geo-marine.com> wrote:
> You have to make the two floors two separate shells and stack them on top
> of each other. You can do this by defining the x y z coordinates on the
> first page of the new shell. You want to make the z coordinate on the
> second shell the same as the height of the first shell. You will also want
> to define the roof of the first floor as below conditioned space and the
> foundation for the second as above conditioned space.
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jamil .
> *Sent:* Sunday, March 06, 2011 7:18 AM
> *To:* equest
> *Subject:* [Equest-users] Different zoning per floor
>
>
>
> Hi folks
>
> I am working on a two story office building, where the layout of the ground
> is not same like the layout of the first floor and accordingly the HVAC
> zoning varies from ground to first floor.
>
> In the schematic wizard, I am facing a problem of defining different zoning
> for each floor, as the program copies the zones of the ground to the first
> and does not allow for editing the first floor zoning.
>
> I managed to define different zones in the detailed design, by editing the
> copied zones in the first floor thru changing the vortices of each zone.
> This method took a considerable amount of time and was pretty confusing.
>
> I was wondering first, if there is a way to define different zoning in the
> first and ground floor in the schematic wizard and second, if there is an
> easier way to change the zoning in the first floor during the detailed
> design.
>
> Thank you in advance
>
> Jamil
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Carol Gardner PE