[Equest-users] Air Flows: minimum design flow

Arpan Bakshi arpanbakshi at gmail.com
Wed Mar 9 12:12:23 PST 2011


Xiaoyang

For baseline, 0.4 cfm/ft2 per G3.1.3.13 or min. ventilation rate,  
whichever is larger.





Arpan Bakshi / YRG
217 Grand 802 NYC
Direct 646.704.2880



On Mar 9, 2011, at 2:57 PM, xiaoyang shi <xs2144 at gmail.com> wrote:

> Hi folks,
>
> Could I ask how to set the "Air Flows: Minimum Design Flow" on the  
> "HVAC Zones: Temperatures and Air Flows" panel? Does ASHARE have  
> this standard?
>
> The Default Minimum Design Flow Value is 0.5 cfm/ft2.  Maybe the  
> value is too high for some instances.
>
> If I set the minimum design flow value is 0.05 cfm/ft2. The output  
> Design flow maybe 0.33cfm/ft2. Then, if I keep on decreasing the  
> value from 0.05 cfm/ft2 to lower values, the output won't change.
>
> So, how can we set Minimum Design Flow value?
>
> Thank you very much.
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG



More information about the Equest-users mailing list