[Equest-users] How best to enter unit heating and cooling loads?
Mark Darrall
MDarrall at a2so4.com
Wed Mar 16 14:34:49 PDT 2011
Thank you, Matt! That also cleared a warning I was getting. Looks like I have a legit baseline run, now – or will, once I get some guidance on the makeup air unit… ☺
MARK DARRALL, AIA, LEED AP BD+C, NCARB
Senior Project Manager
[cid:image001.jpg at 01CBE400.71C63860]
DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN
A2SO4 Architecture, LLC
Union Station
300 South Meridian Street / 250
Indianapolis, Indiana 46225
TEL 317 388 8850
FAX 317 280 0692
MOB 765 749 0841
www.a2so4.com
Please consider the environment before printing this e-mail.
CONFIDENTIALITY NOTICE: This email and any files transmitted with it are confidential and intended solely for the use of the individual or entity to which they are addressed. If you are not the intended recipient, you may not review, copy or distribute this message. If you have received this email in error, please notify the sender immediately and delete the original message. Neither the sender nor the company for which he or she works accepts any liability for any damage caused by any virus transmitted by this email.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of MatthewRLarson at Eaton.com
Sent: Wednesday, March 16, 2011 5:02 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] How best to enter unit heating and cooling loads?
Mark,
In the system properties for your air-side system, you can enter the COOL-SIZING-RATIO and HEAT-SIZING-RATIO under the Cooling and Heating tab right below the COOLING-CAPACITY and HEATING-CAPACITY. So if you want the heating capacity oversized by 25%, you would enter 1.25 for HEAT-SIZING-RATIO.
Thanks,
Matthew Larson, LEED AP BD+C
Project Engineer
Energy Solutions Group
E M C Engineers, Inc.
Eaton’s Electrical Services & Systems
143 Union Blvd, Suite 350
Lakewood, CO 80228
tel: +1 303 328-3419
mobile: +1 303 668-2511
fax: +1 303 974-1239
MatthewRLarson at Eaton.com<mailto:MatthewRLarson at Eaton.com>
www.eaton.com/energysolutions<http://www.eaton.com/energysolutions>
[cid:image002.jpg at 01CBE400.71C63860]
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mark Darrall
Sent: Wednesday, March 16, 2011 2:53 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] How best to enter unit heating and cooling loads?
Hi,
What is the best way to get the oversized capacities for the air-side units? I took the zone loads from a simulation run and multiplied them by the required factors and then plugged them into COOLING-CAPACITY and HEATING-CAPACITY. Is this correct?
SIZING-RATIO – SYSTEM sounds right, but there’s no way to enter different factors for heating and cooling.
Thanks!
MARK DARRALL, AIA, LEED AP BD+C, NCARB
Senior Project Manager
[cid:image001.jpg at 01CBE400.71C63860]
DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN
A2SO4 Architecture, LLC
Union Station
300 South Meridian Street / 250
Indianapolis, Indiana 46225
TEL 317 388 8850
FAX 317 280 0692
MOB 765 749 0841
www.a2so4.com
Please consider the environment before printing this e-mail.
CONFIDENTIALITY NOTICE: This email and any files transmitted with it are confidential and intended solely for the use of the individual or entity to which they are addressed. If you are not the intended recipient, you may not review, copy or distribute this message. If you have received this email in error, please notify the sender immediately and delete the original message. Neither the sender nor the company for which he or she works accepts any liability for any damage caused by any virus transmitted by this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110316/3f657ff7/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 2061 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110316/3f657ff7/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 39998 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110316/3f657ff7/attachment-0005.jpg>
More information about the Equest-users
mailing list