[Equest-users] disabling zone electric heat?
Nick Caton
ncaton at smithboucher.com
Wed Mar 16 14:46:41 PDT 2011
Hey James,
The airflow part is pretty simple I think, but I'm not sure whether
there is a clean way to make an "heating availability schedule" that
would apply only to the zone reheat...
I'd like to think there should be a clean/direct way to pull that off,
but nothing comes to mind... indirectly it might be do-able through a
combination of zone-level thermostat sch tweaks and system level heating
availability schedule & delivery temperature tweaks, but I'm not totally
sure... Hopefully someone else has this fresh in their head to share?
In any case, to define morning warmup airflow as you're describing (100%
open VAV terminals), look to the highlighted field at the zone level:
Here's the associated help entry:
MIN-FLOW-SCH
Takes the U-name of a schedule of TYPE = FRAC/DESIGN whose values are
values of minimum flow ratio. This schedule will override the specified
or calculated value of MIN-FLOW-RATIO unless the schedule value is -999.
In this case the specified or calculated value of MIN-FLOW-RATIO, which
is found on report SV-A for each zone, is used for that hour. This
schedule can be used with a value of 1.0 during warmup periods and -999
for other hours to simulate VAV boxes that are fully open during warmup.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of James
Hansen
Sent: Tuesday, March 15, 2011 1:29 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] disabling zone electric heat?
I've got a project where we have shutoff VAV boxes with electric heat
and RTUs that provide the supply air and have HW heat (mainly for
preheat of OA). The RTUs are also used to provide morning warmup heat.
During the 60 mins or so that morning warmup is occurring, the RTUs send
out 80 degree air, and the electric heat at the shutoff boxes is
disabled (they are forced open 100%).
Has anyone modeled this successfully? If I could disable zone heat for
one hour a day (5:00am-6:00am), I would think the RTU would raise its
supply air temp to compensate. But this is not possible as far as I
know. Thanks for any tips!
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110316/211d935f/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 21666 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110316/211d935f/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110316/211d935f/attachment-0002.jpeg>
More information about the Equest-users
mailing list