[Equest-users] Fresh air heat recovery system in WLHP

Suka leedusersuka at 163.com
Thu Mar 24 02:49:12 PDT 2011


Hi Bruce, thank you for your response. I tryed it(OA Temperature, OA Enthalpy, Dual Temperature, Dual Enthalpy) but still can't use heat recovery.


At 2011-03-21 22:06:02,"Bruce Easterbrook" <bruce5 at bellnet.ca> wrote:
Try going to the first tab, Outside Air and Economizer, down at the bottom of that page there is Air-Side Economizer Cycle, set that up and it should turn on the secondary parameters on the remaining tabs.
Bruce Easterbrook P.Eng.
Abode Engineering

On 21/03/2011 03:07 AM, Suka wrote:

Hi, I have some trouble in eQUEST.

Water loop heat pump system with fresh air heat recovery has been designed for the building. But in eQUEST, fresh air in WLHP system can't use heat recovery.

Anyone who knows how to deal with it please help me. Thanks!

 

 

 Best Regards,

Fiona Xiang
Project Engineer

 

 


This email and any attached files are confidential and copyright protected. If you are not the addressee, any dissemination of this communication is strictly prohibited. Unless otherwise expressly agreed in writing, nothing stated in this communication shall be legally binding.

The ultimate parent company of the Atkins Group is WS Atkins plc. Registered in England No. 1885586. Registered Office Woodcote Grove, Ashley Road, Epsom, Surrey KT18 5BW. A list of wholly owned Atkins Group companies registered in the United Kingdom and locations around the world can be found athttp://www.atkinsglobal.com/terms_and_conditions/index.aspx.

Consider the environment. Please don't print this e-mail unless you really need to.




_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110324/b2a1e15b/attachment-0002.htm>


More information about the Equest-users mailing list