[Equest-users] Simplified Method Glass Conductance Entry

Carol Gardner cmg750 at gmail.com
Thu Mar 24 14:42:27 PDT 2011


Riley,

If the over all U value and SC reported at the end of the LV-D report for
each exposure match yours, I wouldn't worry about it. When you are looking
at each window you are probably seeing some sort of adjustment for area.

Carol

On Thu, Mar 24, 2011 at 2:29 PM, Mehta, Gaurav <Gaurav.Mehta at stantec.com>wrote:

> Use the formula below to convert Glazing U-value to Conductance.
>
>
>
> Conductance = 1/((1/Glazing U)-0.2)
>
>
>
> This formula  is from the DOE-2 Reference manual.
>
>
>
> Best regards,
>
>
>
> Gaurav
>
>
>
> *Gaurav Mehta, LEED® AP BD+C*
> Sustainable Building Analyst
> Stantec
>
> 1932 First Avenue Suite 307
> Seattle WA 98101
> Ph: (206) 770-7779
> Fx: (206) 770-5941
> Gaurav.Mehta at stantec.com
>
> *stantec*.com <http://www.stantec.com>
>
>
>
> The content of this email is the confidential property of Stantec and
> should not be copied, modified, retransmitted, or used for any purpose
> except with Stantec's written authorization. If you are not the intended
> recipient, please delete all copies and notify us immediately.
>
>
>
> ü Please consider the environment before printing this email.
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Riley Beise
> *Sent:* Thursday, March 24, 2011 2:12 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Simplified Method Glass Conductance Entry
>
>
>
> Hi all,
>
>
>
> I’d like to be able to enter my total glazing U values in one place for
> simplicity.  I set my frame widths to zero and defined my window glass type
> in “simplified” where I entered my total window U value in the “Glass
> Conductance” field.  When I check my LV-D report it shows my windows having
> a lower U value than what I entered.  I understand there are some variables
> at play here that are likely the cause (air film resistance and windspeed of
> rating (summer vs winter as shown in the topic help).  I don’t understand
> what is going on here.
>
>
>
> So,
>
>
>
> Can someone shed some light on why my LV-D window U values don’t match my
> “Glass Conductance” value in these circumstances?
>
>
>
> And, how would you recommend I enter my windows if I have the overall U
> value already from product data?
>
>
>
> Thanks
>
>
>
> Riley
>
>
>
> ___________________________________
>
> Riley Beise, EIT, *LEED GA*
>
> Green Building Specialist
>
>
>
> Enermodal Engineering Ltd.
>
> 602-2303 4th St. SW, Calgary AB T2S 2S7
> p. 403-244-0474 ext. 435
>
> f. 403-244-0475
>
> e. rbeise at enermodal.com <bpapau at enermodal.com>
>
> www.enermodal.com
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110324/2eee1bba/attachment-0002.htm>


More information about the Equest-users mailing list