[Equest-users] eQuest: Thermal Storage (Ice Tank)

Josh Greenfield JGreenfield at primerachicago.com
Tue May 24 13:41:01 PDT 2011


I'm modeling an ice storage system...the chilled water system has four
(4) chillers...from 8am to 8pm the four chillers work together to output
40*F leaving CHW after the ice tank is fully discharged...from 8pm to
8am only TWO of the chillers work together to output 24*F leaving CHW to
charge the ice tanks.  Here's what I've done so far to model this
system...

 

*         I've modeled SIX chillers even though there are only
four...the normal 40*F LCHWT operation chillers have an EER of 8.4,
whereas the 24*F LCHWT operation chillers during ice mode have an EER of
7.6, so 4 of the 6 chillers modeled are really just 2 chillers as they
are a 'normal mode' and 'ice mode' for two of the chillers as I have to
have those different EER values in there.  The other 2 chillers are just
'normal mode' as they aren't on during ice charging.

*         I have a charging schedule set up from 8pm to 8am with a value
of '1' and 8am to 8pm with a value of '0'.

*         I have a loop setpoint schedule set up from 8pm to 8am to be
24*F and 8am to 8pm to be 40*F.

 

My question is, how can I schedule the chillers so that the two 'ice
mode' chillers are on from 8pm to 8am, and the four 'normal mode'
chillers are on from 8am to 8pm??  The 'Equipment Controls' only allow
LOAD defined management, and not Time-Of-Day defined management.  And
there also aren't any "Availability" schedule options like there are for
air-side systems.

 

Any suggestions would be very helpful!

 

 


Josh Greenfield, PE <http://www.idfpr.com/dpr/WHO/pe.asp> , REP
<http://www.cityofchicago.org/city/en/depts/bldgs/supp_info/chicago_ener
gy_conservationcodeoverview.html> , LEED AP BD+C
<http://www.gbci.org/main-nav/professional-credentials/credentials.aspx>
, BEMP <http://www.ashrae.org/certification/page/2491> 
Energy Services Manager
Associate Vice President
312.242.6392 Direct
jgreenfield at primerachicago.com

 
Primera Engineers, Ltd.
100 S. Wacker Drive, Suite 700
Chicago, IL 60606
312.606.0910 Main
312.606.0415 Fax
http://www.primerachicago.com <http://www.primerachicago.com/> 



 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110524/5687b129/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1879 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110524/5687b129/attachment.jpeg>


More information about the Equest-users mailing list