[Equest-users] Fixing unmet hours / outside of throttling range warnings

John Aulbach jra_sac at yahoo.com
Mon May 2 10:00:01 PDT 2011


Mark:

Either spread your thermostat throttling range, or incrase your total supply 
airflow.

John R. Aulbach, PE, CEM
Senior Energy Engineer

________________________________

PartnerEnergy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com| jaulbach at ptrenergy.com
 




________________________________
From: Mark Darrall <MDarrall at a2so4.com>
To: equest-users <equest-users at lists.onebuilding.org>
Sent: Mon, May 2, 2011 6:21:24 AM
Subject: [Equest-users] Fixing unmet hours / outside of throttling range 
warnings


Good Morning, eQUESTers,
 
I’m working on my design case model. Here’s my ATTN report:
 
**WARNING**********************************************************************
             SYSTEM EL1 Sys1 (PSZ) (G.NNW1)          may have inadequate cooling 
capability
             Check COOLING-CAPACITY and MIN-SUPPLY-T for consistency
 
**WARNING**********************************************************************
             SYSTEM EL1 Sys2 (PSZ) (G.WSW2)          may have inadequate cooling 
capability
             Check COOLING-CAPACITY and MIN-SUPPLY-T for consistency
 
**WARNING**********************************************************************
             SYSTEM EL1 Sys3 (PSZ) (G.N3)            may have inadequate cooling 
capability
             Check COOLING-CAPACITY and MIN-SUPPLY-T for consistency
 
**WARNING**********************************************************************
             SYSTEM EL1 Sys4 (PSZ) (G.S4)            may have inadequate cooling 
capability
             Check COOLING-CAPACITY and MIN-SUPPLY-T for consistency
 
**WARNING**********************************************************************
             SYSTEM EL1 Sys5 (PSZ) (G.N5)            may have inadequate cooling 
capability
             Check COOLING-CAPACITY and MIN-SUPPLY-T for consistency
 
**WARNING**********************************************************************
             SYSTEM EL1 Sys6 (PSZ) (G.E6)            may have inadequate cooling 
capability
             Check COOLING-CAPACITY and MIN-SUPPLY-T for consistency
 
**WARNING**********************************************************************
             SYSTEM EL1 Sys7 (PSZ) (G.C7)            has zero outside air for 
design calculations
 
 
This last one I can answer as this system is a R/A only computer room cooler. 
For the others:
 
COOLING-CAPACITY comes directly from the HVAC designer and is the capacity of 
the installed units. I’ve tried adjusting MIN-SUPPLY-T from 55 to 50 (and this 
seems to jive with information the coil manufacturer provides) to get a larger 
delta-T and it only seemed to make things worse somehow. Minimum OSA is 20%, but 
again, this is a design condition. These units do have enthalpy-controlled 
economizers.
 
I’m also getting WAY too many hours outside of throttling range – 15%. My 
baseline model only has a 3%. I’m way out of whack with Appendix G requirements.
 
Any suggestions as to settings to modify to clear these? Thank you!
 
MARK DARRALL, AIA, LEED AP BD+C, NCARB
Senior Project Manager
 
 
DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN
 
A2SO4 Architecture, LLC
Union Station
300 South Meridian Street / 250
Indianapolis, Indiana 46225
TEL  317 388 8850
FAX  317 280 0692
MOB 765 749 0841
www.a2so4.com
 
Please consider the environment before printing this e-mail.  
 
CONFIDENTIALITY NOTICE: This email and any files transmitted with it are 
confidential and intended solely for the use of the individual or entity to 
which they are addressed. If you are not the intended recipient, you may not 
review, copy or distribute this message. If you have received this email in 
error, please notify the sender immediately and delete the original message. 
Neither the sender nor the company for which he or she works accepts any 
liability for any damage caused by any virus transmitted by this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110502/43f755dc/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 2061 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110502/43f755dc/attachment-0002.jpg>


More information about the Equest-users mailing list