[Equest-users] Modeling regular curtain wall systems

David Eldridge dse at grummanbutkus.com
Fri May 6 06:51:20 PDT 2011


I think Bill is saying that for each zone surface he would take this
approach, not that he is loading up the zones on the end with extra frame
and walls in the middle zones (if any) with none.



David



*
*



David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP

*Grumman/Butkus Associates*

*
*





*From:* equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Arpan Bakshi
*Sent:* Friday, May 06, 2011 8:03 AM
*To:* Bishop, Bill
*Cc:* equest-users
*Subject:* Re: [Equest-users] Modeling regular curtain wall systems



Sounds like a good compromise. I'm concerned the corner zones would take on
the brunt of the frame/glass disparity, creating a large contrast of skin
loads on the perimeter.





Arpan Bakshi, LEED AP BD+C

YRG sustainability


On May 6, 2011, at 8:35 AM, "Bishop, Bill" <wbishop at pathfinder-ea.com>
wrote:

I typically model curtain walls as a single window per exterior wall
surface, and increase the frame width to make the frame area equal to the
total non-glazed area of the window opening.

I select a glass type from the DOE-2 window library based on the closest
match of U-value and SHGC to the actual glazing selection.



Bill



<image003.jpg>



*From:* equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Arpan Bakshi
*Sent:* Thursday, May 05, 2011 8:29 PM
*To:* Mark Darrall
*Cc:* equest-users
*Subject:* Re: [Equest-users] Modeling regular curtain wall systems



Mark, in the interest of time, you can accomplish what you would like to
through the Building Shell Wizard --



1. If you already have a Window 4/5 file from the manufacturer, attach it in
Wizard Screen 6 under Glass Category.



2. If you do not have this, right-click Glass Category and under Tutorials
and Reference, and navigate to DOE 2 Glass Library (xls). You will be able
to find something comparable to your glass type here. Select a Frame
Typeand Frame
Wd (in) which matches your curtain wall assembly.



3. Under Window Dimensions, Positions and Quantities, you can specify a Typ
Window Width (ft). Now comes the shortcut to avoid Custom Window/Door
Placement. If your fenestration design consists of an irregular, custom
pattern, count the number of vertical mullions you have, and divide the full
width of the curtain wall by that number. Enter that number into Typ Window
Width (ft). Though your curtain wall will not have the same appearance in
the 3D View, you are provided the same length of lineal feet of window
frame, which will result in the same overall assembly U factor.





On Thu, May 5, 2011 at 7:55 PM, Mark Darrall <MDarrall at a2so4.com> wrote:

Thank you! I’m working against a pretty hard deadline and don’t really have
time to learn two more software packages. I found some basis of design
information for both the curtain wall and glazing – can I use manufacturer’s
design guide graphs and calculations? The graphs are “per AAMA 507.” They
also have charts for NFRC 100 overall U factors and NFRC 200 SHGC and VT.



I think the LEED reviewers just want to make sure we’re accounting for the
frames and not just getting COG.



Take care!



MARK DARRALL, AIA, LEED AP BD+C, NCARB
Senior Project Manager



<image004.jpg>



DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN



A2SO4 Architecture, LLC

Union Station
300 South Meridian Street / 250
Indianapolis, Indiana 46225
TEL  317 388 8850

FAX  317 280 0692

MOB 765 749 0841
www.a2so4.com



*Please consider the environment before printing this e-mail*.



CONFIDENTIALITY NOTICE: This email and any files transmitted with it are
confidential and intended solely for the use of the individual or entity to
which they are addressed. If you are not the intended recipient, you may not
review, copy or distribute this message. If you have received this email in
error, please notify the sender immediately and delete the original message.
Neither the sender nor the company for which he or she works accepts any
liability for any damage caused by any virus transmitted by this email.



*From:* Alex Krickx [mailto:akrickx at seriousmaterials.com]
*Sent:* Thursday, May 05, 2011 7:47 PM
*To:* Carol Gardner; Mark Darrall
*Cc:* equest-users
*Subject:* RE: [Equest-users] Modeling regular curtain wall systems



You can create curtainwall systems in Window and Therm – but I don’t believe
that eQUEST will import any of the frame conductance data. I think the best
way to model curtainwall systems is to model the frame in THERM and WINDOW5,
create a DOE2 report file – then import that file into eQUEST and manually
edit the frame width and conductance to match what you calculated in
WINDOW5/THERM.

Alex



Alex Krickx, LEED AP

Building Energy Specialist

<image005.jpg>

1250 Elko Dr, Sunnyvale, CA 94089

(t) 408.541.8124



*Warning:** The information contained in this e-mail may be privileged
attorney-client communications or attorney work product and/or proprietary
and confidential.  If the reader of this message is not the intended
recipient then you have received it in error and any review, distribution or
copying of this message is prohibited and you are to notify us immediately
by reply e-mail and delete the original message immediately.*







*From:* equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Carol Gardner
*Sent:* Thursday, May 05, 2011 4:43 PM
*To:* Mark Darrall
*Cc:* equest-users
*Subject:* Re: [Equest-users] Modeling regular curtain wall systems



Intriguing question. I did just a little looking around and found:
windows.lbl.gov/software/NFRC/NFRCSim6.3-2010-Manual.pdf.*
which is a link to the user manual for Window and Therm. Check it out. You
can create things, windows,etc., maybe even curtainwalls, using Window and
import them into eQUEST

Carol*

On Thu, May 5, 2011 at 4:19 PM, Mark Darrall <MDarrall at a2so4.com> wrote:

Hi!



What’s the best way to input a curtain wall system to allow for the
repetitive vertical mullions? I can calculate system U factor based on the
area of vision glass : overall area, but I don’t see a way to input that
directly…unless:



If the vertical mullions are already captured in the system U factor can I
just ignore it and treat it like one huge picture window? So at FRAME-WIDTH
I would just enter the width and properties of the perimeter frame and then
at GLASS-CONDUCTANCE enter the corrected U-factor for the system?



I did search this in onebuilding.org, but didn’t see it addressed.



Thanks!



MARK DARRALL, AIA, LEED AP BD+C, NCARB
Senior Project Manager



<image004.jpg>



DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN



A2SO4 Architecture, LLC

Union Station
300 South Meridian Street / 250
Indianapolis, Indiana 46225
TEL  317 388 8850

FAX  317 280 0692

MOB 765 749 0841
www.a2so4.com



*Please consider the environment before printing this e-mail*.



CONFIDENTIALITY NOTICE: This email and any files transmitted with it are
confidential and intended solely for the use of the individual or entity to
which they are addressed. If you are not the intended recipient, you may not
review, copy or distribute this message. If you have received this email in
error, please notify the sender immediately and delete the original message.
Neither the sender nor the company for which he or she works accepts any
liability for any damage caused by any virus transmitted by this email.




_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG




-- 
Carol Gardner PE


_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG




-- 





*Arpan Bakshi**  *LEED AP BD+C
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110506/e57cbe5e/attachment-0002.htm>


More information about the Equest-users mailing list