[Equest-users] Return Air Reset Control
Bishop, Bill
wbishop at pathfinder-ea.com
Thu May 12 07:28:00 PDT 2011
Lyle,
Each zone in eQUEST will be modeled as having a single, uniform temperature each hour. In cooling mode, the return air temperature should be the thermostat setpoint from the COOL-TEMP-SCH (assuming the system can meet the loads), or a little hotter from duct/plenum heat gains. You can consider using the system COOL-CONTROL strategies to modulate supply air temperature and/or flow rate. WARMEST is the only value that resets the supply air based on zone loads.
I think you would need CFD software if you wanted to optimize data center HVAC design.
My approach in eQUEST would be to model this as I would any other system - entering known system capacities, flow rates etc., and entering the expected equipment loads into the space. (My experience with a few server rooms is that data center equipment loads are nearly constant 24/7/365. I'd be interested to hear others' experiences.) Even if the actual data center is controlled by hot aisle temperature instead of a wall-mounted thermostat, I would create the thermostat schedule based on a typical data center room setpoint, such as 75°F.
Regards,
Bill
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Lyle Keck
Sent: Wednesday, May 11, 2011 7:46 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Return Air Reset Control
Does anyone have experience modeling return air temperature reset in equest?
I am modeling a data center that resets the supply airflow based on a max return air temperature of 95 degF coming off the hot server aisles.
I searched the archives and the only thread I found on this topic did not have any useful modeling input or guidelines.
Any experience or suggestions are appreciated. Thank you for your time,
Lyle Keck
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110512/7d08738a/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20862 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110512/7d08738a/attachment-0002.jpeg>
More information about the Equest-users
mailing list