[Equest-users] ASHRAE90.1 Baseline System
Paul Riemer
Paul.Riemer at dunhameng.com
Thu May 26 07:22:26 PDT 2011
Praveen,
There is a rationale that ASHRAE 90.1 does not allow tradeoffs between buildings. So if you are using a model to demonstrate compliance with 90.1, you need a model of each building separately.
So for LEED 2009, can the EAp2 10% savings requirement be met in aggregate or does it have to be met on each building independently?
Surely someone has answered that somewhere. Look in the big book.
If aggregate is okay, then I wonder if each building needs to individually state or demonstrate compliance with 90.1?
(or should we forget we thought of that question?)
Thanks for getting me thinking about this. I have a multiple building project on the back burner and maybe I can use this to nudge them.
Paul Riemer, PE, LEED AP
DUNHAM
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Demba Ndiaye
Sent: Thursday, May 26, 2011 8:48 AM
To: Praveen Jain
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] ASHRAE90.1 Baseline System
Praveen,
Assuming you are applying for LEED 2009, you might consult the "2010 LEED Application Guide for Multiple Buildings and On-Campus Building Projects".
This document is available here https://www.usgbc.org/ShowFile.aspx?DocumentID=7987.
There is also another Guide that was published in 2005 I believe and that apply to earlier versions of LEED.
______________
Demba NDIAYE
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bruce Easterbrook
Sent: Thursday, May 26, 2011 9:21 AM
To: Praveen Jain
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] ASHRAE90.1 Baseline System
I have yet to try what you are doing but you would need to treat each building separately. The number of floors in the building will determine your baseline building as Nick pointed out. Your method to deliver conditioned air to each zone in each building is going to be separate even though you may use a plant to provide for example, hot and cold water to both buildings. I haven't looked ahead to see if you are going to run into a system type conflict between the 2 buildings but if you do just use common sense and determine what is the best way to go to maximize energy efficiency. None of the "rules" are written in stone. They are bendable if you have a good argument and can back it up with hard data which eQuest will give you.
Bruce Easterbrook P.Eng.
Abode Engineering
On 26/05/2011 12:07 AM, Praveen Jain wrote:
Thanks for your reply
Nick, I have created both building in one single model to take benefit of shading of building also as one single leed project.
I am still not able to decide while choosing baseline building; number of floors should be sum of all floor in project or maximum number of floor of building.
--
With Regards
Praveen
On Wed, May 25, 2011 at 7:22 PM, Nick Caton <ncaton at smithboucher.com<mailto:ncaton at smithboucher.com>> wrote:
That's what I'd do (but I'd also ask the lists to be sure)!
The only real distinction (and potential for a problem) here is that you have two buildings in one model. Provided you continue to treat each building separately, both in building your baseline and in documentation, I don't see any base reason why a reviewer would reject the models.
Can anyone share a successful 2-building-1-model submittal experience to confirm this alone isn't an issue?
~Nick
[cid:image001.jpg at 01CC1B83.A332C160]
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com<http://www.smithboucher.com>
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of varun kulkarni
Sent: Wednesday, May 25, 2011 6:59 AM
To: Praveen Jain
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] ASHRAE90.1 Baseline System
Prateek,
The first column for table G3.1.1A says for Non residential 5 floors or less and 25,000 SF to 150,000 SF. I think your sytem should fall under this and so Baseline System 6 should be the right choice. I dont know if adding the floors on the two buildings is a good idea !!
Anyone else in support or in disagreement with my comment ?
On Wed, May 25, 2011 at 4:53 AM, Praveen Jain <praveenjain83 at gmail.com<mailto:praveenjain83 at gmail.com>> wrote:
Dear All,
I am working on a project which has two towers within the same LEED boundary. One tower is 3 stories and another is 4 stories. Total conditioned area of the project is 70000 ft2. Heating type of my project is Electric.
In this case, what can be project baseline system? Should I choose baseline system 6 or baseline System 8?
Thanks in Advance
--
with regards,
Praveen K. Jain
Roorkee
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Thanks and Best Regards,
Sincerely,
Varun Kulkarni , M.S. , EIT
Note: Please do not print, unless required.
--
with regards,
Praveen K. Jain
Roorkee
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110526/8e003419/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110526/8e003419/attachment-0002.jpg>
More information about the Equest-users
mailing list