[Equest-users] campus modeling
John Aulbach
jra_sac at yahoo.com
Mon Nov 14 09:58:13 PST 2011
Thanks for a clarifying view, Steve. I come from the world of running DOE-2.1B in a desktop for 12 HOURS !! So a few minutes more run time isn't even on my radar !!
________________________________
From: STEVE SAMENSKI <steve at thespinnakergroupinc.com>
To: John Aulbach <jra_sac at yahoo.com>; kirti pabrekar <arkirtipabrekar at gmail.com>; "equest-users-request at lists.onebuilding.org" <equest-users-request at lists.onebuilding.org>; "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Sent: Monday, November 14, 2011 5:23 AM
Subject: Re: [Equest-users] campus modeling
Kirti --
The method you propose is slightly different than what John recommends. Clicking the multiplier box (your proposal) is really more appropriate for repetitive floors of a tower. What John's recommending is that you create one building and then copy it in the shell Wizard. John's method gives greater accuracy but will require more computation time for your computer. This is probably a good trade-off.
Steve Samenski, PE, LEED AP BD+C, BEMPVice President - Sustainable Technologies
The Spinnaker Group
786-385-3510
www.thespinnakergroupinc.com
From: John Aulbach <jra_sac at yahoo.com>
Reply-To: John Aulbach <jra_sac at yahoo.com>
Date: Mon, 14 Nov 2011 05:49:45 -0800 (PST)
To: kirti pabrekar <arkirtipabrekar at gmail.com>, "equest-users-request at lists.onebuilding.org" <equest-users-request at lists.onebuilding.org>, "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] campus modeling
Kirti:
I have done campuses several times. Each building that is duplicated can use the multiplier method, but each building may have a different orientation and distance between the others. Create Building 1 shell (single story ??), then create the 2nd building (duplicating the 1st building), but then on the 1st screen give it a distance and orientation from the 1st building. If all other parameters are the same in Building 1 as Building 2, you should be fine.
John Aulbach
Partner Energy
________________________________
From: kirti pabrekar <arkirtipabrekar at gmail.com>
To: equest-users-request at lists.onebuilding.org; equest-users at lists.onebuilding.org
Sent: Sunday, November 13, 2011 9:28 PM
Subject: [Equest-users] campus modeling
hi,
i have to model a two campus buildings.
in one case the buildings are such designed that they are independent structures located a distance away from each other. there are four building with stilt parking under each.
and in the second case, the buildings are designed as a closed loop with a small construction joint in them. also in this case there are 12 buildings in all, but 5 prototypes which are repeated to form a closed loop. will checking the shell multiplier tab help in this? i was thinking of using the shell multiplier for buildings with repetitive footprints instead of making all the 12 buildings.
please guide me through.
thanking all in anticipation.
--
Regards,
Ar. Kirti Pramod Pabrekar.
IGBC AP, LEED India,
M. Arch,
Environmental Planning and Design.
...Green is a commitment...not a competition...
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111114/cfc804b8/attachment-0002.htm>
More information about the Equest-users
mailing list