[Equest-users] Underheating warning for bunch of zones

Nikola Kravik NKravik at willdan.com
Wed Nov 30 14:59:51 PST 2011


Rob/all,

I don't have baseboards, it's basic VAV/w reheat system-I was trying to use the baseboards just to see if the zone heating kicks in.
I've attached the zip file, it's giving me the same warning that the zones are under heated and also 1 error that the "hot water loop has zero design flow".

I'm stuck and not sure how to go about it. Please point/help me understand how to go about the error fix....
I appreciate your feedback.

Best,
Nikola
From: Rob Hudson [mailto:rdh4176 at gmail.com]
Sent: Tuesday, November 29, 2011 12:03 PM
To: Nikola Kravik
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Underheating warning for bunch of zones

I would first check your system level inputs.  Have you used a VAV system? if so, you need to know that these systems don't like to use the heating coil in the air handler and therefore you need to specify a reheat coil size and a preheat coil.  Also, if you have baseboards in the model, they don't like to operate very well when set to activate to outdoor conditions.  I always set the baseboard control to thermostat.

Hopefully these few tips help out.

Rob
On Tue, Nov 29, 2011 at 2:52 PM, Nikola Kravik <NKravik at willdan.com<mailto:NKravik at willdan.com>> wrote:
hi,

I'm simulating CHW Plant with CAV AHU's and bunch of packaged/split system units around supporting areas of the hospital/clinic.

I get the warning messages similar to below for almost all my zones  and my gas heating hot water is extremely low, no matter what I try do on the heating side. I added baseboards but it didn't make a difference-still have bunch of zones underheated looking at the ss-o's.
Do you any other hints you can share where else to look for the HHW low consumption?

Best,
Nikola
[cid:image001.png at 01CCAF6F.D62EBE40]
[cid:image002.jpg at 01CCAF6F.D62EBE40]

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>



--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111130/e6a6a85b/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 47313 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111130/e6a6a85b/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 92188 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111130/e6a6a85b/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: HHawk zip.zip
Type: application/x-zip-compressed
Size: 494753 bytes
Desc: HHawk zip.zip
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111130/e6a6a85b/attachment-0002.bin>


More information about the Equest-users mailing list