[Equest-users] more than 10 chillers

Bishop, Bill wbishop at pathfinder-ea.com
Mon Oct 3 06:14:18 PDT 2011


Kimberly,

 

Either create multiple primary CHW loops (as is probably the case for a
building with so many chillers) or combine the chillers in a way that
makes the most modeling sense. With so many chillers, it will be
important to understand how they are (or will be) staged to meet the
load, and to combine their capacities, and prorate their efficiencies
etc. accordingly.

 

Regards,

Bill

 

 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Kimberly Wiebe
Sent: Friday, September 30, 2011 3:48 PM
To: Equest-users at lists.onebuilding.org
Subject: [Equest-users] more than 10 chillers

 

Hello, 

 

A building has 42 air cooled chillers. The maximum number of chillers
that be attached to the primary chw loop is 10. What do you do? 

 

 

Kimberly Wiebe
Graduate Mechanical Engineer
Buro Happold 
801 West Adams Suite 800 
Chicago, IL 60607
USA

Tel: (+1) 312.451.1615

kimberly.wiebe at burohappold.com

www.burohappold.com

 

This message has been scanned by MailController -
portal1.mailcontroller.co.uk | 

This message has been scanned by MailController
<http://portal1.mailcontroller.co.uk/> .

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111003/2fb5f0dc/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 22378 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111003/2fb5f0dc/attachment.jpeg>


More information about the Equest-users mailing list