[Equest-users] Medical equipments
Emtman, Brian
emtman at coffman.com
Tue Oct 25 16:12:00 PDT 2011
Expanding on what Bruce said, consider that equipment nameplate electric
values tend to be substantially higher than in real life. If you are
currently using nameplate equipment values as the basis for your Watts /
sf model inputs, it could be unrealistically increasing both the
electric energy consumption of the equipment itself and the energy
required to condition the space.
FYI, if you have an ASHRAE 2009 Fundamentals Handbook, check out Tables
6 and 7 on pages F18.11 for nameplate and recommended heat gain rates
from typical medical equipment (or see attached). You're probably not
modeling each individual blanket warmer (I hope!) but it gives you an
idea of how substantially actual conditions can differ from nameplate.
As Bruce also mentioned, make sure a utilization schedule is applied to
whatever peak value you come up with so that it is not running at 100%
all the time. It sounds from your email like you may already have a
schedule applied to prevent them from being "used" very often though...
Brian
Brian Emtman, LEED AP BD+C
Mechanical Engineering
Coffman Engineers, Inc.
p 206.623.0717 | f 206.624.3775 www.coffman.com
<http://www.coffman.com/>
LASTING creativity | results | relationships
Please consider the environment before printing this email.
________________________________
From: Fred Betz [mailto:fbetz at aeieng.com]
Sent: Tuesday, October 25, 2011 6:25 AM
To: Bruce Easterbrook; Chen, Ke-Huang
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Medical equipments
Chen,
I do a lot of LEED modeling in health care. You should be seeing between
20% and 35% for the electrical process load.
If you have a lot of large equipment; CT's, MRI's, etc. then you'll be
closer to the 35%. If you have a small clinic or medical office building
that shares equipment between locations, then you'll be closer to 20%.
Another consideration is that your large equipment might be water
cooled. If that's the case, you should put about 10-15% of the electric
load in the space, and then 85-90% of the load as an external load
similar to exterior lights. Make sure to put an equivalent cooling load
on you chilled water loop as a process load.
Hope that helps,
Fred
Fred Betz PhD., LEED AP
Sustainable Systems Analyst
AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI 53719
P: 608.236.1175 | F: 608.238.2614
fbetz at aeieng.com <mailto:fbetz at aeieng.com> | www.aeieng.com
<http://www.aeieng.com/>
From: Bruce Easterbrook [mailto:bruce5 at bellnet.ca]
Sent: Sunday, October 23, 2011 9:35 PM
To: Chen, Ke-Huang
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Medical equipments
Hi Chen,
I don't do much medical work or LEED but the medical equipment should
be modelled like a process load and have it's own schedule you can
manipulate. 60% sounds like a lot. With it's own schedule you can
change it to reflect its actual loads and locations in the building.
Process loads, like industrial loads don't effect LEED. But they do
effect the sizing of your HVAC equipment. So you do have to model them
realistically. You could put them on their own sub meter as well. This
might make separating from the LEED parts of your project simpler. LEED
or not, your building has to work well. That is your primary focus.
60% is a big effect, make sure it is realistic and make sure your
systems can handle it.
Bruce Easterbrook P.Eng.
Abode Engineering
On 23/10/2011 4:35 AM, Chen, Ke-Huang wrote:
Dear eQUEST users,
I am trying to build a LEED Health Care model and have a question about
the electric of medical equipments. After I modeled the equipments, the
electric consumption of Misc. Equip. is about 60% of total electric but
the medical equipments are not used very frequently. Do I have to add
the medical equipments to the model or where can I plan a schedule for
the medical equipments? Did anyone have the experience of modeling a
LEED Health Care model? It's my first time building a Health Care model,
is there anything I need to look over ? Any suggestion will be
appreciated.
Best regards,
KeHuang Chen
System Engineer
IBT Division
Siemens Limited Taiwan
Tel : (+886)2-2652-8888 ext. 896
Mobile : (+886)960548011
Fax : (+886)2-2652-8824
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111025/327ab730/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Medical and Lab Equip Heat Gains.jpg
Type: image/jpeg
Size: 106942 bytes
Desc: Medical and Lab Equip Heat Gains.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111025/327ab730/attachment-0002.jpg>
More information about the Equest-users
mailing list