[Equest-users] fuel oil and boilers

Demba Ndiaye Demba.Ndiaye at setty.com
Tue Sep 13 11:10:23 PDT 2011


Kristin,

Make sure that you define a fuel meter of type "fuel oil" (see enclosed Illustration 1). Then, assign it to the boiler (see second illustration). You should then be able to see the fuel oil usage as "fuel oil" (see third screen capture).

Hope that helps,

_______________
Demba NDIAYE

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kristin Gustafson
Sent: Tuesday, September 13, 2011 9:48 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] fuel oil and boilers

I am running a simulation with a fuel-oil boiler, and have set up a custom utility rate for fuel oil. There is no natural gas on site, the DHW is heated electrically. However, the summary simulation sheets are still reporting the fuel oil usage as "natural gas" . Is there a way around this?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110913/6b4f2812/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Capture.JPG
Type: image/jpeg
Size: 30736 bytes
Desc: Capture.JPG
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110913/6b4f2812/attachment-0006.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Capture2.JPG
Type: image/jpeg
Size: 31014 bytes
Desc: Capture2.JPG
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110913/6b4f2812/attachment-0007.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Capture3.JPG
Type: image/jpeg
Size: 28178 bytes
Desc: Capture3.JPG
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110913/6b4f2812/attachment-0008.jpeg>


More information about the Equest-users mailing list