[Equest-users] floor area used by VAV system
Jeremy McClanathan
jmcclanathan at CDiengineers.com
Sun Sep 18 13:14:59 PDT 2011
When you change the path to ducted, the wizard changes plenum zones to type "Unconditioned" rather than "Plenum". Unconditioned zones are counted in the total area on the SV-A report, plenum zones are not.
Jeremy
___________________________________________
Jeremy McClanathan, P.E., BEMP, HFDP, LEED(r) AP BD+C
[cid:image001.jpg at 01CC7604.DA870410]
4200 194th St SW, Ste 200, Lynnwood, WA 98036
P 425-672-1071 | F 425-778-8769
P Please consider the environment before printing this email.
From: deepika khowal [mailto:deepika.khowal at gmail.com]
Sent: Sunday, September 18, 2011 1:09 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] floor area used by VAV system
Hello all
I am working on a 20 storey office building which has 20125 sf per floor.
I have assigned 1 VAV system /floor area.
I realized that the return air path plays a big role. When I use plenum return (since I have 4ft plenum in my design), the floor area used by system in SV-A report is 20125 sf which is correct.
As soon as I change the path to ducted, floor area doubles.
Does anyone know why this is happening?
Any thoughts will be helpful.
Thanks
Deepika
Results with return air path as plenum- the floor area is correct with plenum return
[cid:image002.jpg at 01CC7604.DA870410]
Results with return air path as ducted- floor area doubles with changing to ducted
[cid:image003.jpg at 01CC7604.DA870410]
This email message, including any attachments, is for the sole use of the intended recipient and may contain confidential, proprietary, and/or privileged information, as well as content subject to copyright and other intellectual laws. If you are not the intended recipient, you may not disclose, use, copy, or distribute the email message or its attachments. If you believe you have received this email message in error, please contact the sender by reply email, immediately delete this email and destroy copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110918/648caccb/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1232 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110918/648caccb/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 37390 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110918/648caccb/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 36258 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110918/648caccb/attachment-0008.jpg>
More information about the Equest-users
mailing list