[Equest-users] Interior Space Temperature

bfountain at greensim.com bfountain at greensim.com
Wed Apr 18 12:08:17 PDT 2012


If the fan schedule is off (and fan control isn't cycle at night) eQUEST doesn't really look at space temp.

My inclination would be to create a psz system serving your space with very small cooling capacity (e.g. 1 BTU/hr -- 0 will cause it to autosize) an an 'always on' fan schedule. Fan volume would depend on whether you wanted to introduce OA. 
Brian Fountain
bfountain at greensim.com

-----Original Message-----
From: Ekaterina Tzekova <ekaterina.tzekova at mail.utoronto.ca>
Sender: equest-users-bounces at lists.onebuilding.orgDate: Wed, 18 Apr 2012 18:38:35 
To: equest-users at lists.onebuilding.org<equest-users at lists.onebuilding.org>
Subject: [Equest-users] Interior Space Temperature

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG





More information about the Equest-users mailing list