[Equest-users] BDL Error
Chris Jones
cj at enersave.ca
Mon Aug 6 10:37:41 PDT 2012
The Split system single is PSZ, or PTAC or UH but these systems are
the same in that the first zone on the system cannot be unconditioned
unless another, conditioned zone is explicitly defined as the CONTROL-ZONE.
Did you intend that each zone have a single system serving it? Are
the spaces to be heated some other way or are the spaces ventilated only?
It would be helpful if you could explain the proposed design HVAC
configuration.
At 08:44 AM 06/08/2012, ramesh buddhi wrote:
>Hi Cris
>
>Thanks a lot for your reply, In the model I had not specified the
>PSZ system, I had assumed Split system single zone(No Heating).
>
>Thanks
>Ramesh BR
>
> New No.110 / Survey No. 151/1, Mahatma Gandhi Road
> Thiruvanmiyur, Chennai 600041 INDIA
> Web: www.greenevolution.in
> Land: +91-44-4201-8369
> Cell : +91-99406-19915
>
>
>From: Chris Jones <cj at enersave.ca>
>To: ramesh buddhi <ramesh at greenevolution.in>; eQuest Users
><equest-users at lists.onebuilding.org>
>Sent: Monday, 6 August 2012 5:29 PM
>Subject: Re: [Equest-users] BDL Error
>
>Ramesh
>The PSZ system requires a CONTROL-ZONE if there is more than one
>zone on the system. If one conditioned zone is not named as the
>CONTROL-ZONE then the first zone after the system definition is
>assumed to be the control zone. A control zone cannot be unconditioned.
>
>The fix is to enter Detailed Edit mode, change to Air Side HVAC,
>select the System and name the Control Zone - from the list, I
>selected EL1 SSW as it is the only conditioned zone on the system.
>
>The file opens correctly but I don't believe you can switch back to
>the Wizard Mode.
>
>At 07:35 AM 06/08/2012, ramesh buddhi wrote:
>>Dear Folks
>>
>>I had modeled an nine storey office Building Iam getting an BDL
>>error that zone is inconsistent with definition: The reference
>>expected a definition as TYPE= Conditioned. I designed this as an
>>unconditioned. How to get rid of this error? Please kindly help me
>>on this. I had attached the files for your reference along with the
>>weather file.Thanks a lot in advance.
>>
>>Thanks
>>Ramesh BR
>>
>> New No.110 / Survey No. 151/1, Mahatma Gandhi Road
>> Thiruvanmiyur, Chennai 600041 INDIA
>> Web: <http://www.greenevolution.in/>www.greenevolution.in
>> Land: +91-44-4201-8369
>> Cell : +91-99406-19915
> >>
>Christopher Jones, P.Eng.
>Suite 1801, 1 Yonge Street
>Toronto, ON M5E1W7
>Tel. 416-203-7465
>Fax. 416-946-1005
>email cj at enersave.ca
>
>>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120806/5d84ad18/attachment-0002.htm>
More information about the Equest-users
mailing list