[Equest-users] Commercial Foodservice Equipment in Energy Model
Nick Caton
ncaton at smithboucher.com
Tue Aug 14 11:24:25 PDT 2012
This is a new resource to me - good find! Here's a brief take:
1. A googled foodservice definition: "Idle Rate - The rate of oven energy consumption while it is maintaining or holding at a stabilized operating condition or temperature. Also called standby energy rate."
I would liken such figures to "installed watts" for lights - this figure would represent hourly operating consumption at a steady state.
2. Efficiency figures are something you might utilize if you intend to model (and document) differing process loads for the baseline and proposed models, to claim credit for utilizing high efficiency equipment. That seems what this resource was built to accommodate.
I don't see anything in this specific excel chart resembling guidance for an operation schedule. Note for heavy foodservice/kitchen modeling, consult with the mechanical designer to address the process sensible/latent load factors for the energy model (i.e. how much heat is removed from the internals by hoods and such).
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ömer Moltay
Sent: Tuesday, August 14, 2012 10:00 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Commercial Foodservice Equipment in Energy Model
Dear All,
I am trying to model foodservice equipment as process energy. I have read previous messages on the forum and have reached the energy consumption table at http://www.fishnick.com/design/resources/leed/.
However, analyzing the table, I have trouble understanding what the idle rate and efficiency concepts really mean and how to convert them into eQuest language (meaning installed power x fraction schedule). Can I use the idle rate as a normalized power consumption rate during one hour? Is this table sufficient by itself to determine energy consumption or do I need to know other data? What use does equipment efficiency have in modeling input?
Thank you,
Ömer Moltay, LEED AP BD+C, ASHRAE BEMP, ASHRAE CPMP, BREEAM Assessor Mimta EkoYapi Hekimsuyu Cad. 559. Sk. No:39
34255 Kucukkoy Istanbul
Tel: 90-212-617-2296
Fax: 90-212-617-2297
www.eko-yapi.net
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Equest-users
mailing list