I would also check the elevation your project is at in eQuest. I had a
project in CO that was at 5,900 ft and eQuest used a altitude-adjustment
factor on all my inputs of 1.24 to account for this and it tripped me up
for a while. I think this was being applied to capacities and airflow rates
I specified.
-Neil
On Thu, Aug 9, 2012 at 12:02 PM, Maria Karpman <
maria.karpman at karpmanconsulting.net> wrote:
> I would check that all applicable sizing ratios are set to 1. The specified
> heating capacity of an air-side system will be adjusted by Heating Sizing
> Ratio entered on Heating -> Coil Cap / Control tab, and Sizing Ratio
> entered on Basics tab of the Air-Side HVAC System Parameters window.
>
> Good luck,
>
> Maria
>
> -----Original Message-----
> From: equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of GK
> Pandian
> Sent: Thursday, August 09, 2012 11:24 AM
> To: equest-users
> Subject: [Equest-users] Simulation output report file
>
> Folks,
>
> In one of my project, I have specified capacity of heating system in
> proposed model, but same doesn't reflect in the simulation output report
> file. Any idea??
>
> Thanks
> GK
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2012.0.2197 / Virus Database: 2437/5189 - Release Date: 08/09/12
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
--
*Neil Bulger*
Project Engineer****
*________________________________*****
I N T E G R A L****
* ** **GROUP*****
** **
427 13th Street, Oakland CA 94612
510 663 2070 x 235
nbulger at integralgroup.com
www.integralgroup.com****
*DEEP GREEN Engineering.*
*________________________________*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120817/2a3723ec/attachment-0002.htm>
More information about the Equest-users
mailing list