[Equest-users] Huge envelope changes having small affect on energy savings
Ron Pecarina
rp.esdc at gmail.com
Wed Aug 22 13:43:54 PDT 2012
>From what I see from these input files, the zone AC/Hr went from 0.2 to
0.8. I did not note a change in any R-value from 4 to 20. The increased
ventilation load is the likely culprit.
On Wed, Aug 22, 2012 at 1:42 PM, Lee Chorney <leec at alliedconsulting.net>wrote:
> Hi Guys,
>
> Here all the .inp files. 1.inp is the base and 2.inp is the proposed.
>
> Thank you,
>
> Lee
>
>
> On Wed, Aug 22, 2012 at 12:48 PM, Lee Chorney <leec at alliedconsulting.net>wrote:
>
>> Hi All,
>>
>>
>> I recently did a model where I had the same system in both base and
>> proposed but I changed the R-Value from 4 (base) to 20 (proposed). I also
>> changed the window U-value from .80 (base) to .35 (proposed). After I did
>> the run, I saw only a 5% savings between the heating and cooling use in the
>> model. When I looked at the loads I saw the base had twice as much cooling
>> and heating load than the proposed. Does any know why the energy savings
>> would only be 5% when you have a huge difference between the cooling and
>> heating loads?
>>
>> Thanks,
>>
>> Lee
>>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Ron Pecarina, PE, CEM, LEED-AP BD&C
Energy and Sustainable Design Consultants, Inc.
1128 Noblewood Drive
Billings, MT 59101
406-208-0227
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120822/46f2f20c/attachment-0002.htm>
More information about the Equest-users
mailing list