[Equest-users] Negative Cooling Energy
Bishop, Bill
bbishop at pathfinder-ea.com
Mon Aug 27 11:50:16 PDT 2012
Eric,
I found at least one problem - you are using a HW reset temperature control on your CHW loop. (Check the week and day schedules on "ChW Reset".) I changed it to an ASHRAE CHW reset schedule and got this:
[cid:image001.jpg at 01CD8462.F2704D80]
Regards,
Bill
[Senior Energy Engineer 28Jun2012]<mailto:wbishop at pathfinder-ea.com>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eric O'Neill
Sent: Monday, August 27, 2012 2:12 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Negative Cooling Energy
I looked around and found a few threads with people experiencing a similar issue as I'm experiencing right now, however, it sounds like their issues may have involved using custom efficiency curves (which I am not). The issue is - I'm getting negative cooling energy, particularly during the shoulder economizer months. I either need help identifying this novel energy source so I can patent it and become filthy rich, or figure out how I broke DOE2...
[cid:image003.jpg at 01CD8462.F2704D80]
If it helps, the effect is exaggerated when I change the economizer lockout from 65F to something lower like 45F (this is where I took the above screenshot).
Has anyone seen this before or found a resolution? I'm guessing (well, hoping) that it's something trivial that I am overlooking, but a weekend away from the model hasn't helped...
I'm attaching the project files. Any thoughts would be appreciated!
Eric O'Neill
608.785.3328 | MICHAELS ENERGY
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120827/7f3e9144/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 24032 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120827/7f3e9144/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 20869 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120827/7f3e9144/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 29342 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120827/7f3e9144/attachment-0008.jpg>
More information about the Equest-users
mailing list