[Equest-users] Help - excessive electricity for space heating

Rob Hudson rdh4176 at gmail.com
Mon Aug 27 13:41:33 PDT 2012


Just looking at your INP file quickly, it appears you have several electric
unit heaters that are trying to keep spaces heated to the same 72 degree
temperature as the rest of the building.  You may want to put those spaces
on a separate schedule with a lower thermostat setting as they are
unoccupied and not necessary to keep at high temperatures unless desired by
owner.  Those systems should also be taken off of any fan schedule so they
only turn on when necessary to reach space setpoints.  if you eliminate the
schedule, make sure to turn on the option of night cycling without OA.

Hope this helps,

Rob

On Mon, Aug 27, 2012 at 4:25 PM, Michael Campbell <
mike at sustainablesolutionscorporation.com> wrote:

> Hello,
>
>
>
> I’m having some trouble with my simulation – I’m currently working on this
> for a LEED project and I’m putting the proposed design together. I think
> I’m at the point where I’m about finished with the proposed design.  When I
> run the simulation, it is showing almost as much electric used for heating
> as I’m using for cooling – the problem is that nearly the entire building
> uses gas heat.  Can someone help me out here?
>
>
>
> Thanks
>
>
>
> *Mike Campbell, EIT, LEED AP O+M
> Sustainability Specialist*
>
> (610) 569-1047 office
>
> (610) 569-1040 fax
>
> mike at sustainablesolutionscorporation.com
>
> www.SustainableSolutionsCorporation.com<http://www.sustainablesolutionscorporation.com/>
>
>
>
> [image: Description: cid:image002.jpg at 01C81E05.97C02180]
>
>
>
> [image: Description: WBE_cmyk_CP copy] [image: Description:
> E_BCorp_logo_POS]
>
>
>
> *This email message and any attachments are for the sole use of the
> intended recipient(s) and may contain confidential and privileged
> information. Any unauthorized review, use, disclosure or distribution is
> prohibited. If you are not the intended recipient, please contact the
> sender by reply email and destroy all copies of the original message and
> any attachments.*
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120827/8a81e4a0/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4667 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120827/8a81e4a0/attachment-0006.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2004 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120827/8a81e4a0/attachment-0007.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2905 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120827/8a81e4a0/attachment-0008.jpeg>


More information about the Equest-users mailing list