I am modeling an elementary school for LEED purposes, and currently
appealing for the EA Prerequisite 2.
In the baseline model:
My zones are supplied by several AHUs, each delivering an amount of air
that includes both re-circulated and fresh air. When determining the
baseline fan power, I am using the attached excel sheet. The supply air
(column C) includes the fresh air (column E) plus return air (Column F).
This sheet gives me the total supply kW/CFM in (Column N). The question
is:
In eQUEST, given that my supply kW/CFM includes the return air, do I
need to zero out any return fans kW when inputting the AHU parameters?
My thought is that I must put them as zero, because I would be double
counting the return air consumption if I didn't.
Best regards,
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Nahas Building, 4th floor
Georges Haddad Avenue
Postal Code: 2028 5806, Saifi District
Beirut, Lebanon
Tel: +961 (0) 1 971 266
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0)207 939 0989
Fax: +44 (0)207 939 0981
Website: www.ecoconsulting.net <http://www.ecoconsulting.net/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120213/5f278663/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 7393 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120213/5f278663/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: IC - Appendix G Fan Power Calculator v2.xls
Type: application/vnd.ms-excel
Size: 42496 bytes
Desc: IC - Appendix G Fan Power Calculator v2.xls
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120213/5f278663/attachment.xls>
More information about the Equest-users
mailing list