Riad,
Q1- You can specify the selected fan capacity (cfm,static
pressure,...etc) in proposed model.
Q2- I do consider whole building unmethours should be <300 hrs. To see
the unmet hours,go to Air-Side HVAC / Summary. The last column "Hours
outside throttling range" represents the unmet hours.(attached screen
shot)
Hope this is helps.
Thanks
GK
On 2/16/12, RIAD ABED <riad_abed at hotmail.com> wrote:
>
> Dear All e-Quest Users
>
> Please If someone can help :
>
> 1- for Sizing Ratio : 1.15 (for Cooling – Equipment Efficiencies) , it
> should applied be for Baseline Model only ? or also it should be in Proposed
> Model ?
> 2- for Umnet Load Hours it should be under 300 Hours for Each Room/Zone ? or
> For the Total Building ? & where I can find the Umet Load Hours in e-Quest
> simulation Report
>
> Thanks by Advance for all of u …….
>
> My Regards,
> Riad el Abed
> Chief MEP , LEED GA,PQP
> ASHRAE MEMBER
> Tel +96170 643977
> www.riadabed.com
>
> DEC Consultants
> Po Box 26330
> Abu Dhabi
> Tel +9712 4457505
> Fax +9712 4457506
> www.dec.ae
> _____________________________________________________________________
> DISCLAIMER
> This email and any files transmitted with it are confidential and intended
> solely for the use of the individual or entity to whom they are addressed.
> If you have received this email in error please notify the sender. Please
> note that any views or opinions presented in this email are solely those of
> the author and do not necessarily represent those of DEC Consultants.
> Finally, although efforts were made to prevent virus transmission, the
> recipient should check this email and any attachments for the presence of
> viruses. DEC Consultants accepts no liability for any damage caused by any
> virus transmitted by this email.
-------------- next part --------------
A non-text attachment was scrubbed...
Name: unmet hours.bmp
Type: image/bmp
Size: 3888054 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120216/0c1d573f/attachment-0001.bin>
More information about the Equest-users
mailing list