[Equest-users] Dummy Zone & DOAS with heat wheel recovery

Sami, Vikram Vikram.Sami at perkinswill.com
Fri Feb 3 08:17:13 PST 2012


You can add a latent internal load too. For cooling - I think if you assign a negative value to the internal source that should work.  The challenge is to get the scheduling correct for the load.

As a side note (if your DOAS is supplying neutral air - ignore this) - if you are supplying air that is significantly cooler than setpoint temperatures (60 degrees & cooler would probably qualify) you need to represent the cooling effect of the DOAS air into the room. You can do this with a negative internal load in the space with an assigned schedule too.


Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462    f: 404.892.5823       e: vikram.sami at perkinswill.com   www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will.  Ideas + buildings that honor the broader goals of society


From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Riemer
Sent: Friday, February 03, 2012 10:44 AM
To: 'Brian Fountain'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Dummy Zone & DOAS with heat wheel recovery

Don't forget humidity!

Paul Riemer, PE, LEED AP BD+C
DUNHAM

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brian Fountain
Sent: Friday, February 03, 2012 9:19 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Dummy Zone & DOAS with heat wheel recovery

Note that at this point, the OA-FROM keyword is just setting the OA temperature for the borrowing system to the return air temperature for the lending system.  It isn't really modelling DOAS yet.  The issue this leads to is the heat recovery device is seeing the exhaust air stream temperature from the dummy zone, not the borrowing zones.

In heating dominated climates, this can be overcome by either adding a dummy internal load to the dummy zone to give it a higher return air temp for heat recovery or what I do is use the frost control to force the exhaust air stream temperature up to a reasonable value (73F) and put that as electric heat on a separate, free meter.  In a cooling dominated climate, I don't know how you would force that dummy zone return temperature down.



On 2/3/2012 7:44 AM, Soham Babu wrote:


*         Create Dummy space & dummy zone

*         Create DOAS as system as package single zone assign to dummy Zone

*          For other system outside air from DOAS.

From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of RIAD ABED
Sent: Friday, February 03, 2012 2:46 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Dummy Zone & DOAS with heat wheel recovery

Dear All e-Quest Users

Please how to model a Dummy Zone & DOAS with heat wheel device (dedicated outdoor outside air) in e-Quest....I need it please very urgent ...if somebody please help me.....Your reply is very very highly appreciated ...thanks by Advance

My Regards,
Riad el Abed
Chief MEP , PQP
Tel  +96170 643977

DEC Consultants
Po Box 26330
Abu Dhabi
Tel +9712 4457505
Fax +9712 4457506
www.dec.ae<http://www.dec.ae>
_____________________________________________________________________
DISCLAIMER
This email and any files transmitted with it are confidential and intended solely for the use of the individual or entity to whom they are addressed. If you have received this email in error please notify the sender. Please note that any views or opinions presented in this email are solely those of the author and do not necessarily represent those of DEC Consultants. Finally, although efforts were made to prevent virus transmission, the recipient should check this email and any attachments for the presence of viruses. DEC Consultants accepts no liability for any damage caused by any virus transmitted by this email.



_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120203/0a4d5291/attachment-0002.htm>


More information about the Equest-users mailing list