[Equest-users] Infiltration & Whole Building air leakage ????
Nathan Miller
nathanm at rushingco.com
Wed Feb 8 07:44:17 PST 2012
This is one of those areas where the wizard is still useful. If you input
infiltration in the DD wizard Building Envelope Constructions screen, it
will automatically calculate infiltration based on exterior wall area
(Ive never checked to see if it includes exterior roof in the calculation
as well, but it doesnt appear so).
Note that 0.4 CFM/SF is not the proper value to input here, because that
is a high static pressure for testing purposes. In my local energy code,
the following conversion factor is given:
If you have already left the wizard, you might want to save another copy
of your project, go back into the wizard to play with the infiltration
rates, and then use the spreadsheet view of Detailed Edit to copy and
paste the infiltration rates the wizard calculates for you. This works
well if you havent changed the order of the spaces or added many new
spaces since you left the wizard.
Sincerely,
Nathan Miller, PE, LEED AP BD+C
Mechanical Engineer/Senior Energy Analyst
O 206-285-7100 | D 206-788-4577
<http://www.rushingco.com/> www.rushingco.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of RIAD ABED
Sent: Wednesday, February 08, 2012 4:54 AM
To: equest-users at lists.onebuilding.org equest-users at lists.onebuilding.org
Subject: [Equest-users] Infiltration & Whole Building air leakage ????
Dear All e-Quest Users
Whole Building air leakage shall not exceed 0.4 CFM/ft² @ 0.3" w.g (2
L/s/m² @ 75Pa) .
So if I consider whole Building air Leakage = 0.4 CFM/ft2 , How can I
Express it in e-Quest , to calculate the Infiltration Value for each space
in the Building , especially in Detailed mode ????
Note : in detailed mode for each Space , we have to put a data for
Infiltration CFM/ft² , but ft² is for floor area not building envelope
area)
.please any help is very appreciated especially who have Big
Experience please
thanks for all
My Regards,
Riad el Abed
Chief MEP , PQP
Tel +96170 643977
DEC Consultants
Po Box 26330
Abu Dhabi
Tel +9712 4457505
Fax +9712 4457506
www.dec.ae
_____________________________________________________________________
DISCLAIMER
This email and any files transmitted with it are confidential and intended
solely for the use of the individual or entity to whom they are addressed.
If you have received this email in error please notify the sender. Please
note that any views or opinions presented in this email are solely those
of the author and do not necessarily represent those of DEC Consultants.
Finally, although efforts were made to prevent virus transmission, the
recipient should check this email and any attachments for the presence of
viruses. DEC Consultants accepts no liability for any damage caused by any
virus transmitted by this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120208/61a115c6/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 33257 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120208/61a115c6/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 14861 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120208/61a115c6/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 54379 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120208/61a115c6/attachment-0008.png>
More information about the Equest-users
mailing list