[Equest-users] Humdity control

Brian Fountain bfountain at greensim.com
Wed Feb 22 05:45:53 PST 2012


Set max humidity keyword to 55%.  Supply air temperature will be reset 
down for humidity control down to minimum supply air temperature if 
required.  Set reheat delta T and heating source -- and watch for 
underheated hours if there is insufficient reheat.

On 2/22/2012 7:27 AM, sambhav tiwari wrote:
> Hi All,
>            I have a VAV system where duct heaters are installed to
> control  space humidity if exceeds 55% how can i model it .
>
> Thanks
> Sambhav Tiwari
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG



More information about the Equest-users mailing list