[Equest-users] What should be put the Sensible Ht fraction in SDW?
Vern Smith
vernon.a.smith at gmail.com
Wed Feb 29 14:17:41 PST 2012
Hello Jing,
Table 23 in the BARB report includes the estimated annual energy use for
each appliance. I suggest developing an average sensible and latent
fraction by multiplying the annual energy for each appliance by the its
sensible and latent fractions. Sum these for all appliances and then
divide the sensible sum and the latent sum by by total annual energy
use. This should give you representative sensible and latent fractions.
Regards,
Vern
_______________________
Vernon A. Smith, P.E.
Smith Energy Engineers, LLC
720-320-9154
On 12:59 PM, Jing Hong wrote:
> Hi all,
> When i was trying to put the sensible Ht (frac) in cooking loads
> section, i met a problem. I followed the Building America Research
> Benchmark (BARB) to define my model. In that case, I should put the
> Sensible load fraction of Refringerator, Dishwasher, range showed on
> BARB into my equest model. However, those appliances has different
> fraction, but i have only one blank for the sensible fraction of
> kitchen in eQuest. How could I decide what number I should choose to
> put in? Did some one use Benchmark to build eQuest model before can
> help me? I am appreciated.
> Jing
More information about the Equest-users
mailing list