[Equest-users] CT Recirc air and quantifying energy penalty in equest for increased entering WB Temp

Nikola Kravik NKravik at willdan.com
Wed Jul 18 15:55:35 PDT 2012


Hi,
I have a project designed with a WSHP/Fluid cooler where the 2 cell FCooler was put in a "cage of wall" (so neighbors don't hear the sound db's).

Well the sound may be lower, but they have bigger issues with the recirc air and elevated wet bulb around the tower, contractor did measurements and instead of 72F EAWB is about 77F.
95/85 design though with the wet bulb at 77-78F, tower is doing 101/91F+.

I tried to quantify the penalty for the decreased capacity (or the other way around the get savings if we knock the wall and bring the db back to 72F) by playing with the approach temp (from the design 13F to 19F) under the FCooler but that didn't make a difference.

Then I tried the CW loop, elevating the CHW Temp to simulate increased FCooler Leaving supply temp from designed 85F to 90+F and that yield about 100Kwh savings but now sure if this is the right way to do it in equest -has anybody attempted something similar in equest and got justifiable results? Would you recommend doing it some other way in equest?

Thank you,
Nikola


[cid:image003.png at 01CD64EF.44FA7B40]
[cid:image006.jpg at 01CD64F4.2ADB37E0]
[cid:image008.jpg at 01CD64F4.2ADB37E0]
Nikola Kravik, LEED AP [cid:image001.gif at 01CD64ED.96442ED0]
Project Engineer

Willdan Energy Solutions
6130 Stoneridge Mall Road, Suite 380
Pleasanton, CA 94588
T. 925.416.4200 ext. 1228
D. 925.416.4228
C. 925.719.5883
F. 925.737.0174
nkravik at willdan.com<mailto:nkravik at willdan.com>
www.willdan.com/energy<http://www.willdan.com/energy>

[cid:image002.jpg at 01CD64ED.96442ED0]

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120718/5bf5040a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 1348 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120718/5bf5040a/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 3030 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120718/5bf5040a/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 45085 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120718/5bf5040a/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 76198 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120718/5bf5040a/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 49465 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120718/5bf5040a/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEM-2_CT Recirc air.zip
Type: application/x-zip-compressed
Size: 462684 bytes
Desc: EEM-2_CT Recirc air.zip
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120718/5bf5040a/attachment.bin>


More information about the Equest-users mailing list