Nikola,
How about using a weather file from a more tropical location that more closely matches your actual conditions?
Keith Swartz, PE, LEED AP
Senior Energy Engineer | Energy Center of Wisconsin | Madison.Chicago.Minneapolis
608.210.7123 | www.ecw.org<http://www.ecw.org/>
From: Nikola Kravik [mailto:NKravik at willdan.com]
Sent: Thursday, July 19, 2012 12:12 PM
To: Robby Oylear
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] CT Recirc air and quantifying energy penalty in equest for increased entering WB Temp
Hi Robby,
Thanks for your email. We will do trending but was hoping that we can also get some numbers out of equest.
Has anybody else even tried to model the below?
Best,
Nikola
Nikola Kravik, LEED AP [cid:image001.gif at 01CD65C7.D3DCE9A0]
Project Engineer
Willdan Energy Solutions
6130 Stoneridge Mall Road, Suite 380
Pleasanton, CA 94588
T. 925.416.4200 ext. 1228
D. 925.416.4228
C. 925.719.5883
F. 925.737.0174
nkravik at willdan.com<mailto:nkravik at willdan.com>
www.willdan.com/energy<http://www.willdan.com/energy>
[cid:image002.jpg at 01CD65C7.D3DCE9A0]
From: Robby Oylear [mailto:robbyoylear at gmail.com]
Sent: Wednesday, July 18, 2012 4:21 PM
To: Nikola Kravik
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] CT Recirc air and quantifying energy penalty in equest for increased entering WB Temp
This might be a situation where you want to use actual energy readings. If they have a consistent load (or maybe you can false load the system somehow) you could take power readings or run some trends at night when the "effective" wet bulb in that built-up well would be closer to what you'd see if the tower was open to ambient air. Compare the two power usage measurements/trends and there's your savings.
If the tower fans have VFD's you should already have power metering capability.
Robby Oylear, PE, LEED AP
Mechanical Engineer
Senior Energy Analyst
D 206-788-4571
www.rushingco.com<http://www.rushingco.com/>
On Wed, Jul 18, 2012 at 3:55 PM, Nikola Kravik <NKravik at willdan.com<mailto:NKravik at willdan.com>> wrote:
Hi,
I have a project designed with a WSHP/Fluid cooler where the 2 cell FCooler was put in a "cage of wall" (so neighbors don't hear the sound db's).
Well the sound may be lower, but they have bigger issues with the recirc air and elevated wet bulb around the tower, contractor did measurements and instead of 72F EAWB is about 77F.
95/85 design though with the wet bulb at 77-78F, tower is doing 101/91F+.
I tried to quantify the penalty for the decreased capacity (or the other way around the get savings if we knock the wall and bring the db back to 72F) by playing with the approach temp (from the design 13F to 19F) under the FCooler but that didn't make a difference.
Then I tried the CW loop, elevating the CHW Temp to simulate increased FCooler Leaving supply temp from designed 85F to 90+F and that yield about 100Kwh savings but now sure if this is the right way to do it in equest -has anybody attempted something similar in equest and got justifiable results? Would you recommend doing it some other way in equest?
Thank you,
Nikola
[cid:image003.png at 01CD65C7.D3DCE9A0]
[cid:image004.jpg at 01CD65C7.D3DCE9A0]
[cid:image005.jpg at 01CD65C7.D3DCE9A0]
Nikola Kravik, LEED AP [cid:image001.gif at 01CD65C7.D3DCE9A0]
Project Engineer
Willdan Energy Solutions
6130 Stoneridge Mall Road, Suite 380
Pleasanton, CA 94588
T. 925.416.4200 ext. 1228<tel:925.416.4200%20ext.%201228>
D. 925.416.4228<tel:925.416.4228>
C. 925.719.5883<tel:925.719.5883>
F. 925.737.0174<tel:925.737.0174>
nkravik at willdan.com<mailto:nkravik at willdan.com>
www.willdan.com/energy<http://www.willdan.com/energy>
[cid:image002.jpg at 01CD65C7.D3DCE9A0]
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120719/eddca99d/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 1348 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120719/eddca99d/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 3030 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120719/eddca99d/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 45085 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120719/eddca99d/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 76198 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120719/eddca99d/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 49465 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120719/eddca99d/attachment-0008.jpg>
More information about the Equest-users
mailing list