[Equest-users] LEED system 5
R B
slv3sat at gmail.com
Tue Jun 5 13:10:41 PDT 2012
I ran the file you sent - it has heating consumption values, unmet hours is
just 200. Strange thing is that the % of hours should be 2.2% or so,
instead it is 8.2% - not sure why that is happening - may be the calc
procedures have changed for the % calcs?
-Rohini
On Tue, Jun 5, 2012 at 2:37 PM, Matt Clough <mclough at kme-inc.com> wrote:
> I have attached the .pd2 and .inp for the baseline building. ****
>
> ** **
>
> I have changed the reheat deltaT, but this has not decreased the unmet
> hours (which explains the lack of energy used for heating)****
>
> ** **
>
> I’m fiddling with HMAX-FLOW-RATIO at the suggestion from the archives, and may try increasing the boiler capacity incrementally.****
>
> But I’m feeling pretty stuck on this one. Just have to keep reading.****
>
> ** **
>
> Thanks for the help****
>
> ** **
>
> *From:* Sami, Vikram [mailto:Vikram.Sami at perkinswill.com]
> *Sent:* Tuesday, June 05, 2012 10:13 AM
> *To:* Nick Caton; Howe, Timothy; Matt Clough;
> equest-users at lists.onebuilding.org
> *Subject:* RE: LEED system 5****
>
> ** **
>
> **1. **Make sure your systems are set to cycle on any****
>
> **2. **Make sure you have your reheat Delta T Set correctly. ****
>
> ** **
>
> This should take care of the problem – otherwise its probably something
> more sinister. ****
>
> ** **
>
> * *
>
> *Vikram Sami*, LEED AP BD+C****
>
> Sustainable Design Analyst****
>
> 1315 Peachtree St. NE, Atlanta, GA 30309****
>
> t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com
> www.perkinswill.com****
>
> *Perkins+Will.* Ideas + buildings that honor the broader goals of society
> ****
>
> ** **
>
> ** **
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Nick Caton
> *Sent:* Tuesday, June 05, 2012 10:57 AM
> *To:* Howe, Timothy; Matt Clough; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] LEED system 5****
>
> ** **
>
> Unmet heating hours will probably go away once you get your heating
> operational. I’d caution against internally justifying/rationalizing one
> set of unmet hours with another – keep in mind unmet hours are an
> indicator/symptom of a problem, not a problem in and of themselves.****
>
> ** **
>
> For HW consumption, open both models and review the DHW loop, schedules,
> process loads, and equipment. Generally everything should be identical
> excepting HW heater efficiency inputs.****
>
> ** **
>
> Reheat coils are set up at the terminal units (zone inputs). Those
> relying on wizards can easily miss some required edits to make reheat
> operate correctly – see attached discussion from the [Bldg-sim] archives
> for a recap.****
>
> ** **
>
> ~Nick****
>
> ** **
>
> ** **
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, P.E.*
>
> SENIOR ENGINEER****
>
> ** **
>
> Smith & Boucher Engineers****
>
> 25501 west valley parkway, suite 200****
>
> olathe, ks 66061****
>
> direct 913.344.0036****
>
> fax 913.345.0617****
>
> www.smithboucher.com* *****
>
> ** **
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Howe, Timothy
> *Sent:* Tuesday, June 05, 2012 9:26 AM
> *To:* Matt Clough; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] LEED system 5****
>
> ** **
>
> Post the .pd2 and .inp file for this project and we may be able to help
> you better.****
>
> ** **
>
> *Timothy Howe, MS, LEED® AP BD+C*
> Mechanical Engineer
> Stantec****
>
> 61 Commercial Street
> Rochester NY 14614
> Ph: (585) 413-5347
> Fx: (585) 272-1814
> Cell: (585) 330-8681****
>
> *stantec*.com <http://www.stantec.com> ****
>
> ****
>
> The content of this email is the confidential property of Stantec and
> should not be copied, modified, retransmitted, or used for any purpose
> except with Stantec's written authorization. If you are not the intended
> recipient, please delete all copies and notify us immediately.****
>
> ** **
>
> ü Please consider the environment before printing this email. ****
>
> *From:* equest-users-bounces at lists.onebuilding.org [
> mailto:equest-users-bounces at lists.onebuilding.org<equest-users-bounces at lists.onebuilding.org>]
> *On Behalf Of *Matt Clough
> *Sent:* Tuesday, June 05, 2012 10:24 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] LEED system 5****
>
> ** **
>
> Salutations!****
>
> ** **
>
> I just completed a LEED model, but after reviewing the data results, I
> think something is wrong.****
>
> ** **
>
> The baseline building is showing no energy used for space heating, heat
> rejection, and service water heating. I have the 2 boilers modeled, per
> G3.1.3.2. This sort of makes sense because the model was showing high
> unmet heating hours, while the proposed building had had unmet cooling
> hours (successfully resolved). ****
>
> ** **
>
> I set up the system 5 equipment (Packaged VAV with reheat) in the wizard,
> but it doesn’t seem to show a heating component in the DDE. I’m going to
> keep looking, but wanted to see if someone could point me in the right
> direction.****
>
> ** **
>
> Regards,****
>
> Matt Clough****
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120605/00622887/attachment-0001.htm>
More information about the Equest-users
mailing list