hrv/erv savings are all about controls. the default setting is on when
system fans are on. this can easily cost you more money & energy than
not having the erv at all.
if the project is not designed for the hrv to operate on a delta t
between the exhaust air & outside air this isn't really obvious. i
suggest changing the control type to delta t & try a few different
amounts. 10 d f, 15 d f, 20 d f & see what the results are. these can
also be set up with an eem so you don't have to keep changing the main
system & seeing what the results are.
look in the march 2012 ashrae journal. there's an article explaining
how to control a total energy wheel & the 2nd paragraph or so actually
says an uncontrolled erv can result in more energy & more cost. though
you only have an hrv the concepts in the article will still apply for
heating mode of course.
On 6/7/12 9:16 AM, Samantha MacHardy wrote:
>
> Hello!
>
> I'm working on modeling a Student Learning Centre and am having a bit
> of trouble with modeling an HRV. I go to the Air-Side HVAC and edit
> the Heat Recovery to say:
>
> Device Installed -- Yes
>
> Device Type: Sensible HX
>
> Effectiveness: 0.7
>
> with everything else left as defaults to each of my systems. In my end
> results, my Domestic Hot Water and Space Heating are over 97% better,
> and my cooling is 50% worse than the reference. These numbers aren't
> making sense but I can't find much help anywhere with HRV in EQuest.
> Any help you could provide would be great!
>
> Thanks!
>
> *Samantha MacHardy*, B. Arch. Sci.
>
> Energy Analyst
>
> Provident Energy Management Inc.
>
> T: 416-736-0630 x 2983 | smachardy at pemi.com <mailto:smachardy at pemi.com>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120607/5e2e06c0/attachment-0002.htm>
More information about the Equest-users
mailing list