[Equest-users] Can't get unmet hours under control for cooling
Howe, Timothy
Timothy.Howe at stantec.com
Fri Jun 8 04:40:28 PDT 2012
Jamie,
Yes based upon what you have indicated that you want to do with it you can do as Dana noted:
· Set to OA at a zone level and use the Minimum Air Schedule schedule with the -999 during on hours to have the system base it upon the zone inputs and 0.01 during off hours to allow economizer to be active when the system cycles.
If you need to simulate DCV you can do as I indicated and create a varying flow based upon occupancy levels using the fraction of design flow for each hour. This would not apply to you baseline model as DCV would not be included.
You did not have the OA defined at the zone level in the model so I did not want to confuse things in my original response with telling you to do so if you were not planning on doing this.
Hope this helps.
Tim.
Timothy Howe, MS, LEED® AP BD+C
Mechanical Engineer
Stantec
61 Commercial Street
Rochester NY 14614
Ph: (585) 413-5347
Fx: (585) 272-1814
Cell: (585) 330-8681
stantec.com<http://www.stantec.com>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
From: Dana Etherington [mailto:Dana.Etherington at crbusa.com]
Sent: Thursday, June 07, 2012 6:33 PM
To: Armstrong, Jamie; Howe, Timothy; equest-users at lists.onebuilding.org
Subject: RE: Can't get unmet hours under control for cooling
Jamie,
I ran into this same issue recently. You can use the same OA for all but set the 'ON' hours to -999. This will ignore the schedule for that hour and the zone calculations and inputs will control.
FRAC/DESIGN accepts a value which is the fraction of the design quantity. Typical values range between 0.0 and 1.0. An entry of -999 causes the schedule to be ignored for that hour.
For example, in the SYSTEM:MIN-AIR-SCH, an entry of 0 or 1 will force the outdoor-air ratio to be 0% or 100% respectively. A value of -999 will cause the schedule to be ignored for the hour, and the outdoor-air ratio will be set by other calculations.
Dana
Mr. Dana Etherington, E.I.T., LEED AP BD+C | CRB | One Kendall Square Ste B2202 | Cambridge, MA 02139
Main: 617-475-3050 | Direct: 617-475-3061 | Mobile: 617-583-3009 | Fax: 617-475-3052 | Ext: 6061
Email: dana.etherington at crbusa.com<mailto:dana.etherington at crbusa.com> | www.crbusa.com<http://www.crbusa.com/>
________________________________________________________________________________________
This document may contain confidential information and is intended for use by the addressee only. If you are not
the intended recipient, please do not transmit, copy, disclose, or utilize this communication in any manner. If you
received this message in error, please notify the sender immediately and delete this message.
ü Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org]<mailto:[mailto:equest-users-bounces at lists.onebuilding.org]> On Behalf Of Armstrong, Jamie
Sent: Thursday, June 07, 2012 6:20 PM
To: Howe, Timothy; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Can't get unmet hours under control for cooling
In regards to OA for PSZ RTU's.
When allowing eQuest to autosize the airflow to each space if you set a ratio of OA to supply air whatever eQuest calculates the supply air needed for that space will vary the outside airflow.
If I enter the OA at the zone level to each space how do you set up a schedule for the OA? Based on Timothy's answer I would need a different schedule for each RTU with its ratio of OA to supply air. I wanted the MinOA schedule to be an on/off flag to deliver the OA that I put in at the zone level according to the occupied schedule.
Jamie Armstrong P.E.
Mechanical Engineer
[cid:image001.jpg at 01CD4549.49D3F850]
v. 210.546.0200 | www.dbrinc.com<http://www.dbrinc.com>
From: Howe, Timothy [mailto:Timothy.Howe at stantec.com]<mailto:[mailto:Timothy.Howe at stantec.com]>
Sent: Thursday, June 07, 2012 3:51 PM
To: Armstrong, Jamie; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: Can't get unmet hours under control for cooling
Jamie,
You have some inconsistencies in your inputs for the OA on system RTU-2 (and all the rest). See highlighted area below. You are saying that the system is 100% recirc by setting the Minimum Outside Air ratio to 0.00, but your Minimum Air Schedule (note that this is a fraction of the design supply CFM type of input) is saying otherwise and takes precedence causing it to be a 100% OA system. See my snip from the hourly reports below too. You need to develop the proper ventilation rates for each system and verify with hourly reports. Do not rely on the summary tab in the air side system tab of eQUEST to give you correct data at all times. If you just define the OA by using the Minimum Outside Air ratio, you will be supplying OA every time the fan operates. To prevent this you need to set up Minimum Air Schedule for each system which is based upon the proper fractions for that system.
[cid:image002.png at 01CD4549.49D3F850]
[cid:image003.png at 01CD4549.49D3F850]
Timothy Howe, MS, LEED® AP BD+C
Mechanical Engineer
Stantec
61 Commercial Street
Rochester NY 14614
Ph: (585) 413-5347
Fx: (585) 272-1814
Cell: (585) 330-8681
stantec.com<http://www.stantec.com>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Armstrong, Jamie
Sent: Thursday, June 07, 2012 4:23 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Can't get unmet hours under control for cooling
I need some help getting these cooling unmet hours under control. I have to get this model complete and submitted by tonight.
We've tried multiple things to try to get the model to work out.
We've tried the following:
· Letting eQuest autosize the heating and cooling for the PSZ units
· Verified that the schedules are consistent with both cooling, heating, and occupancy.
· On the baseline building we have the min cfm set to 0.5 for most spaces and 1 cfm/sf for some of the larger spaces.
· We set the PSZ -fan - flow parameter - indoor fan mode to intermittent to get the unit to show partial capacity thru out the days.
One item is RTU-2 in my model. It serves only one space. We have a high amount of unmet hours on this and we are letting it auto size the capacity and airflow and it still says its not staying under control. We're assuming that we are missing one small check box that's somehow causing these unmet hours.
I've attached the pd2 files for both baseline and proposed along with weather data and inp files.
Thanks in advance for any help!
Jamie Armstrong P.E.
Mechanical Engineer
[cid:image001.jpg at 01CD4549.49D3F850]
v. 210.546.0200 | www.dbrinc.com<http://www.dbrinc.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120608/ad44ea2f/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4860 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120608/ad44ea2f/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 27954 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120608/ad44ea2f/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 63033 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120608/ad44ea2f/attachment-0005.png>
More information about the Equest-users
mailing list