[Equest-users] Gas INFRA-RED radiant heater
Pasgar, Arash
APasgar at dbrinc.com
Fri Jun 8 08:46:48 PDT 2012
Thank you Tim.
To make it more clear. I have a 2500 sf shop without any cooling and just gas infra-red radiant for heating.
I think I have no other choice to select unit heater for proposed plan an just over ride the cfm to 10 as you said and enter the heating capacity.
I think I need to do exactly the same for baseline. Am I correct?
Thank you,
Arash Pasgar
Mechanical Designer
[Description: Description: Description: Description: Description: Description: image001]
v. 210.546.0200 | www.dbrinc.com
From: Howe, Timothy [mailto:Timothy.Howe at stantec.com]
Sent: Friday, June 08, 2012 10:24 AM
To: Pasgar, Arash; equest-users at lists.onebuilding.org
Subject: RE: Gas INFRA-RED radiant heater
I would model the radiant heater as baseboard and set you supply fan in the proposed to something low like 10 CFM and put in 0 for the supply fan power. Also if this space is not cooled, I would use a thermostat schedule for cooling that is high enough that the cooling never turns on.
In the baseline remove the baseboard. Let the CFM autosize and set the fan power to the allowable kW/cfm as specified in Appendix G.
Tim.
Timothy Howe, MS, LEED® AP BD+C
Mechanical Engineer
Stantec
61 Commercial Street
Rochester NY 14614
Ph: (585) 413-5347
Fx: (585) 272-1814
Cell: (585) 330-8681
stantec.com<http://www.stantec.com>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasgar, Arash
Sent: Friday, June 08, 2012 11:13 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Gas INFRA-RED radiant heater
Hi all,
I have a Gas INFRA-RED radiant heater in a big space. I tried to model it as a unit heater, heat source=furnace, enter heating capacity same as my mechanical sch.
Under SA-V report shows a lot of CFM for fan that is wrong in my case, because there is no supply fan.
How can I fix this in my propose and baseline plan.
Thank you,
Arash Pasgar
Mechanical Designer
[Description: Description: Description: Description: Description: Description: image001]
v. 210.546.0200 | www.dbrinc.com<http://www.dbrinc.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120608/86f86f26/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 4870 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120608/86f86f26/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 4870 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120608/86f86f26/attachment-0005.jpg>
More information about the Equest-users
mailing list