This is true. Unless the DOE-2 weather processor (doewth, wth.f) has
been upgraded for DOE-2.2, it is not Y2K compliant (nor is DOE-2.1X
itself, for that matter). What I've been doing for years has been to
reset the years > 20XX to 19XX. Please note that this does not affect
the contents of the weather file at all. Other deficiencies in the
DOE-2 weather processor and format are:
1) fails at latitudes > 62.5 or < -62.5, i.e., above the Arctic or
below the Antarctic Circles because the routine for determining sunrise
fails.
2) temperatures and solar radiation are stored in integer F or
BTU/hr-ft2, wind direction in octals, wind speed in 0.1 knots, etc.,
causing round-off errors
especially when the input weather data are in SI units.
I've made numerous changes to the DOE-2 weather processor to overcome
these limitations, while keep the file format compatible with the
original DOE-2 *.BIN format, but minor changes would also be needed in
doesim to access or read these enhancements, but I haven't made any
effort to promote such changes.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga, CA 94556
(o) (925)388-0265 (c) (510)928-2683
www.whiteboxtechnologies.com
"Building energy simulations at your fingertips"Joe Huang
On 6/19/2012 7:25 AM, Jonathan Bowser wrote:
> I don't know if this helps, but maybe it'll spark a thought by someone on here...
>
> I've recently played with the DOE-2 Processor for weather conversion. I was rummaging around the source code and found comments in the code that basically stated one of the algorithms for computing information that is dependent on the earth's position about the sun were only valid between the time between March 1, 1900 and December 31, 1999 for time zones east of the international date line.
>
> Why is that the case? I don't really know, but maybe someone else can chime in and provide some insight on a workaround for you.
>
> -- Jon
>
>
> -----Original Message-----
> From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Chris Jones
> Sent: Tuesday, June 19, 2012 9:08 AM
> To: equest-users at lists.onebuilding.org
> Subject: [Equest-users] DOE22 weather processor
>
> I am making a TRY weather file for 2011.
>
> The INP file doesn't like dates above 1999.
> PACK
> TRY Vancouver -999
> TRY 71892 -999 8 49.18123.1830-BITNORMAL 4 20. .025
>
> I can use -999 and it works but if I put 2011 the processor quits and tells me:
> --- ERROR --- YEAR IS OUTSIDE ALLOWED RANGE. THE ALLOWED
> RANGE IS -1 TO 1999. PROCESSING WILL BE TERMINATED.
>
> Any ideas?
>
>
> >>
> Christopher Jones, P.Eng.
> Suite 1801, 1 Yonge Street
> Toronto, ON M5E1W7
> Tel. 416-203-7465
> Fax. 416-946-1005
> email cj at enersave.ca
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
--
Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D
Moraga, CA 94556 (o) (925)388-0265 (c) (510)928-2683
www.whiteboxtechnologies.com "Building energy simulations at your
fingertips"
More information about the Equest-users
mailing list