[Equest-users] Existing Building Constructions modeled for LEED
Ross Farris
RFarris at glumac.com
Thu Jun 21 14:00:26 PDT 2012
Bill,
Thanks for the response. For now I am going to leave the walls insulated in both models. I may keep digging a bit further to see if anyone has taken credit for interior construction insulation in the past.
As for the systems. Yes, I have the Data Centers on PSZ systems. The "out of whack" that I was referring to was too much heat being transmitted through the slab to the floors below and that heat wasn't being accounted for when the system for the floor below was sized based on the loads within its assigned spaces. Therefore, the systems for the adjacent spaces to the data center (both below and beside) had cooling hours out of range. Some spaces were never going below 85 degrees so I had to force up to 5 CFM/sf(min design flow) into some of the spaces to make the system autosize properly. Inputting the proper insulation eliminates these issues.
As for your points regarding both educating the client about the design conditions acceptable for a data center and regarding energy savings from the heat recovery and conditioning for the data center, yes definitely. I couldn't agree more.
Thanks again for the insight!
Regards,
Ross
Ross Farris
Energy Analyst
GLUMAC | 415.398.7667
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Thursday, June 21, 2012 6:03 AM
To: Ross Farris; equest-users at lists.onebuilding.org
Subject: RE: Existing Building Constructions modeled for LEED
Ross,
I've always modeled partitions identically for the baseline and proposed models, even for existing buildings. The wording in Appendix G is "For existing building envelopes, the baseline building design shall reflect existing conditions..." Interior partitions are not part of the building envelope, and are not covered in the Building Envelope Requirements Tables 5.5 in ASHRAE 90.1. If you are insulating the walls around the data center, I would do the same in both the baseline and proposed models.
You didn't elaborate on what "out of whack" means for the HVAC systems. In case you are not already doing it, the data center should be modeled in the baseline with its own single-zone system per G3.1.1. If the concern is that the data center is so cold that it is causing heating in adjacent spaces, you could use this opportunity to educate the design team/client regarding recent research that shows data centers don't have to be kept as cold as conventional wisdom has dictated. Don't forget that the data center constitutes a large process load that should be modeled identically in the baseline and proposed models, and that this offers an opportunity for energy savings through heat recovery, efficient cooling, etc.
Regards,
Bill
[cid:image001.png at 01CD4FA4.6B4E3210]<mailto:wbishop at pathfinder-ea.com>
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ross Farris
Sent: Wednesday, June 20, 2012 7:12 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Existing Building Constructions modeled for LEED
Greetings everyone,
I am going to be modeling an existing building as a "major renovation" under LEED NC 2009. Per the App G Guidelines, I will be using all of the constructions that exist in the existing building as opposed to creating constructions as per 90.1 for the baseline model. However, I have come across an interesting situation that I have not dealt with previously. We will be adding a large data center to an interior space on the top floor, which is currently just office space. Currently there is no insulation in the walls and floors surrounding this new data center and it is throwing the HVAC systems assigned to adjacent spaces way out of whack. Though I would like to be able to take some credit for properly insulating the interior constructions surrounding the new data center, it doesn't seem appropriate to leave the baseline with completely uninsulated interior walls and floors.
I am wondering if anyone has come across this issue in the past and how you may have handled it. Please feel free to contact me directly if you need more information or have any questions. Thanks in advance for your comments.
Cheers,
Ross Farris, CEPE
Energy Analyst
[http://www.glumac.com/glumacsig.gif]<http://www.glumac.com/>
________________________________
[40 yr color small]
150 California Street, 3rd Floor
San Francisco, CA 94111
T. 415.398.7667 ext.4083 F. 415.398.0596
Thinking. Inside the building.
[cid:image001.png at 01CC45FA.A3365810]<http://www.twitter.com/glumacengineers>[cid:image004.jpg at 01CC98A3.24F9BEA0]<http://www.facebook.com/pages/Glumac/213797265436>[cid:image002.jpg at 01CC45FA.A3365810]<http://www.linkedin.com/company/34034>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120621/e34b075c/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 21646 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120621/e34b075c/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.gif
Type: image/gif
Size: 6582 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120621/e34b075c/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 11793 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120621/e34b075c/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 896 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120621/e34b075c/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 823 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120621/e34b075c/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 843 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120621/e34b075c/attachment-0008.jpg>
More information about the Equest-users
mailing list