[Equest-users] DCV fan power LEED question?
Shaun Martin
smartin at shaunmartinconsulting.com
Tue Jun 26 09:54:52 PDT 2012
Hi Laura,
An exhaust system that has no heating or cooling is required to be modeled
identically in the baseline and proposed (p 174, 90.1-2004). In other
words, you would have a separate, direct supply serving this exhaust system.
Both supply and exhaust should be the same in both models.
But, if I understand correctly, you have a process exhaust fan that extracts
air from a conditioned space intermittently (via the packaged CV unit). The
process load represented by this exhaust must be modeled identically in both
models. That would include the fan energy and any heating + cooling loads.
Shaun
Shaun Martin LEED AP
Principal
Shaun Martin Consulting
2060 Pine Street
Vancouver, BC V6J 4P8
P: 604-789-1095
E: smartin at shaunmartinconsulting.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Laura Howe,
RCE
Sent: 25-Jun-12 10:47 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] DCV fan power LEED question?
Can anyone else comment on this? I'm not sure I'm on the right track at
all, why does LEED want me to model a fan system identically (below I
question the supply but now I'm questioning why model identically the
exhaust)? Isn't the only requirement for identical fan modeling if the
space is not heated nor cooled? I see some discussion in the archives on
this type of language, but can't find any results of where the modeler went.
Maybe it is because it is Monday morning, but I seem to be questioning where
I thought they were going with these comments. We plan to send in some
questions, but I want to ensure my questions aren't limiting their response
by presupposing anything. Perhaps they are just confused because we've got
multiple systems serving the same space, and being modeled as one?
Thanks
From: Laura Howe, RCE [mailto:laurahowe.rce at qwestoffice.net]
Sent: Friday, June 15, 2012 12:30 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] One more fan power EIR and DCV question
HI Again all-
Thanks for everyone for their assistance earlier this week, it really helped
me progress with this model adjustment. I am currently at another dilemma.
This is DCV not for typical occupancy, but for ventilating infrequent diesel
fumes.
I have two systems modeled as one, a constant volume packaged unit along
with an exhaust system (no heating/cooling). The exhaust system will
operate separate from the packaged unit and the proposed case includes a
fraction in the operation schedule to reflect DCV operation. That schedule
doesn't affect the package unit except it will have less heating/cooling
load due to the DCV. I don't see the DCV affecting the fan sizing or
operation of the baseline packaged unit. The packaged unit is constant
volume. So, the LEED comments refer to identically modeling the base and
proposed systems, for fan volume and fan power, on this exhaust system.
I've worked out matching the exhaust system well enough, but now I'm
wondering if I need to match the supply also. The simplistic answer would
be "yes", even if the comments refer only to the exhaust system I am
concerned a cursory review may still not be happy with the supply fan
volume/power not matching. I think not matching is valid and it is
definitely more favorable, so that's what I'd rather do.
The baseline system has a larger supply fan, and will have a greater
heating/cooling load (no DCV). The proposed system will have a smaller
supply fan and a smaller heating/cooling load. I think the base case fan
sizing is more accurate since it is based on the actual loads of the
baseline building. If I use the fan sizing/power from proposed, the project
will take a big hit. Basically I think this means in theory that not
matching the supply fans, even though they are tied to the exhaust DCV, is
an accurate estimation of savings from baseline to proposed.
Right now I'm inclined to leave the supply not matching, and provide an
explanation. However since there has already been one review, I don't like
the potential that they will just come back with a response of eliminating a
certain number of points. If they don't think my response is adequate, I
don't think they will give me another chance, correct?
For those that requested their actual response, I finally got my hands on a
document I could copy text:
1. "The Baseline fan power calculations and the SV-A reports for the
Baseline model indicate that the exhaust fan systems (SF-1 and SF-2, as
indicated in the mechanical schedules provided for PI Form 4: Schedule and
Overview Documents) have not been modeled identically in the Proposed and
Baseline cases. All independent fan systems of the HVAC systems in the
actual design must be modeled identically between the Proposed and Baseline
models at actual equipment capacities (fan volume and fan power) as required
by Table G3.1.10 in the Proposed building column, since the fan design air
flow rates and fan power per Sections G3.1.2.8 and G3.1.2.9, respectively,
only applies to system types 1 through 8 in Table G3.1.1A. Revise the
Proposed and Baseline model so all independent fan systems of the HVAC
systems are modeled identically between the Proposed and Baseline model. In
addition, provide revised SV-A reports for the Proposed and Baseline model
reflecting the changes.
Thoughts? Must I go simplistic and make supply match? Am I offbase
thinking not matching is a valid energy consumption model comparison?
Thanks
Laura