[Equest-users] 答复: what's the default equipment control?
John Aulbach
jra_sac at yahoo.com
Thu Mar 22 07:58:07 PDT 2012
Joey:
For your "default" case, you will note chiller-1 and chiller-2 total runs hours total 2750 hrs. I would check if you are shutting off chiller -1 and going to chiller-2 for some reason. i would have thought it to be as i originally surmise (i.e., sharing the load at each junction).
________________________________
From: "Jiao, Joey" <Joey.Jiao at WSPGroup.com.cn>
To: John Aulbach <jra_sac at yahoo.com>; Equest-users at lists.onebuilding.org
Sent: Wednesday, March 21, 2012 11:48 PM
Subject: 答复: [Equest-users] what's the default equipment control?
Hi John & everyone:
Thank you for your helps , I just check that, but it seems different than we thought.
The PS-H report show the chiller water loop run hours. I add it in the form, so you can get it clear.
Equipment control Chiller 1a Chiller 1b Chiller 1c Chiller Water Loop
None 2126 624 607 2750
Chiller1~3 to seq 1~3 2750 607 0 2750
All Chillers seq 1 2750 2750 2750 2750
Now you can find that , the loop run hours for all control types is 2750.
If the default control type as we thought , the chiller 1a should be 2750 equal tothe run hours of Chiller Water Loop, because in any situation , the chiller 1ashould first and always be used.
Maybe I think too much. But it is a software , I think there must be a sample and clear way for the default control.
Thank you for your help again.
Joey
发件人:John Aulbach [mailto:jra_sac at yahoo.com]
发送时间: 2012年3月22日 13:20
收件人: Jiao, Joey; Equest-users at lists.onebuilding.org
主题: Re: [Equest-users] what's the default equipment control?
Joey:
I am guessing, but I BELIEVE Chiller-1 gets to a certain load (think it's defined in the chiller setup), then Chiller-1 and Chiller-2 share the load until Chiller-3 is needed, when all three share the load.
See if that makes sense.
John Aulbach
Partner Energy
________________________________
From:"Jiao, Joey" <Joey.Jiao at WSPGroup.com.cn>
To: Equest-users at lists.onebuilding.org
Sent: Wednesday, March 21, 2012 7:49 PM
Subject: [Equest-users] what's the default equipment control?
Hi, everyone:
What’s the default equipment control when a loop with more than 1 plant?
At first I think the default should be” chiller1a- sequence 1, chiller 2a-sequence2, …” or all the chillers with the same sequence 1.
But my experiment shows it different than my think .
I make a system with 3 chiller and make a calculation under different control way.
The result run hour shows below:
Equipment control Chiller 1a Chiller 1b Chiller 1c
None 2126 624 607
Chiller1~3 to seq 1~3 2750 607 0
All Chillers seq 1 2750 2750 2750
So I’m puzzled with how should the software control more than 1 plant when there is no equipment control set?
Any suggestion should be appreciated.
Thank you very much.
Joey
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120322/fecec839/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 6739 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120322/fecec839/attachment-0002.png>
More information about the Equest-users
mailing list