[Equest-users] Warehouse with heating in cooling in base and proposed. Same envelope requirements?
Karen Smith
skaren758 at gmail.com
Fri Oct 26 06:13:06 PDT 2012
Good afternoon,
Im trying to find out the following maybe you guys can help me out here.
I’m currently modeling a facility of a total of 47,600 SF including a
28,000 SF Warehouse. The facility includes 2 levels of offices, breakrooms,
etc and a double height warehouse adjacent to them. The proposed design is
composed of 2 AHUs, one for the first floor, one for the second and an
only heating and ventilation system based on 2 boilers for the warehouse.
According to this, the baseline should be a System 5 Packaged VAV with
Reheat, Packaged rooftop VAV with reheat, Direct expansion cooling type and
Hot-water fossil fuel boiler for heating. One system per floor. FYI, we
tried the whole addenda “dn” thing but it did not work because the
allowance of fan power for the warehouse area was extremely low, so we kept
the normal compliance path. However, when this is the case, we would have
to model the baseline and proposed warehouse with both heating and cooling.
(specified on Table G3.1) same system 5; but my question would be in terms
of envelope. Would they have to be classified as regular non-residential R
values for the proposed? Shouldn’t both baseline and proposed warehouse
have the same u- values as well? Should they be classified as semiheated
envelope values, since in reality this is a warehouse and the
owner/architect are not really counting on putting insulation in this area?
I would appreciate your suggestions and interpretation.
[image: Inline image 1]
_______________________________________________
Trace-users mailing list
http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121026/84fac6d8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 138594 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121026/84fac6d8/attachment.png>
More information about the Equest-users
mailing list