[Equest-users] How we can change interior floor reflectivity of the building model in the eQuest?
Uday Gorre
u_k_gorre at ateindia.com
Tue Oct 9 21:43:49 PDT 2012
Dear Nimesh,
Select the emissivity of the surface and then use the below table for inside
film resistance value in surface construction> layers tab in terms of inside
film resistance that shows the reflectivity of the surface faces to inner
side of the space.
Regards
Uday Kumar
INSIDE-FILM-RES
Specifies the combined convective and radiative air film resistance for the
inside wall surface. The default of 0.68 hr-ft2-F/Btu (0.1198 m2-K/W) is an
appropriate value for vertical walls. For horizontal surfaces, such as
ceilings and floors, the suggested inside film resistance can be found in
Table 12 <JavaScript:TL_10732.HHClick()> . Because only one value is allowed
for each surface, you should decide which is more important, cooling or
heating.
For radiant barriers having a low-emissivity surface (for example, aluminum
foil or insulation with aluminum coating) facing the interior of the space,
select the emissivity from Table 13 <JavaScript:TL_10733.HHClick()> and
then determine the INSIDE-FILM-RES value by interpolating the e=0.09, e=0.20
and e=0.05 columns of Table 12 <JavaScript:TL_10734.HHClick()> .
Table 12
INSIDE-FILM-RES values for position of surface, direction of heat flow and
insidesurface emissivity.
Position of surface
Direction of heat flow
Surface emissivity
0.90*
0.20**
0.05***
Ceiling in the heating mode
or Floor in the cooling mode
Horizontal
Up
0.61 (0.11)
1.10 (0.19)
1.32 (0.23)
45( slope
Up
0.62 (0.11)
1.14 (0.20)
1.37 (0.24)
Vertical
Horizontal
0.68 (0.12)
1.35 (0.24)
1.70 (0.30)
45( slope
Down
0.76 (0.13)
1.67 (0.29)
2.22 (0.39)
Ceiling in the cooling mode
or Floor in the heating mode
Horizontal
Down
0.92 (0.16)
2.70 (0.48)
4.55 (0.80)
*Regular building materials: wood, masonry, non-metallic paints, paper
**Polished aluminum coated paper, for example
***Bright aluminum foil, for example
>From 1997 ASHRAE Fundamentals, p.24.2
If you cannot decide which is more important, cooling or heating, you can
use the average of the heating and cooling values. For exterior walls and
roofs, the outside-film-resistance is calculated by the program depending on
wind speed. For interior walls, the air film described in INSIDE-FILM-RES is
the film on the side of the wall that is in the SPACE where the wall is
specified. For the calculation of the U-Value of an INTERIOR-WALL, the
INSIDE-FILM-RES is duplicated on the other surface (opposite side).
Table 13 IR Emissivity of Different Interior Surfaces
Surface
Emissivity
Aluminum foil, bright
0.05
Aluminum sheet
0.12
Aluminum coated paper, polished
0.20
Steel, galvanized, bright
0.25
Aluminum paint
0.50
Regular glass
0.84
Building materials
(wood, masonry, non-metallic paints)
0.90
>From 1997 ASHRAE Fundamentals, p.24.2
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
nimesh.prajapati
Sent: 10 October 2012 8:37 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] How we can change interior floor reflectivity of the
building model in the eQuest?
Dear Friends,
I want to change interior floor reflectivity of the building model in the
eQuest. To do this I am opting to detailed edit model and going to " EL1IFLr
Construction " but there shows ext. colour ( abs).
So my question is - How we can change interior floor reflectivity of the
building model in the eQuest?
Can you please guide me?
Thanks,
Nimesh Prajapati
(+91 9687133492)
HVAC Design Engineer & Energy Modeller
Description: Description: C:\Users\nimesh.prajapati\Desktop\CADD.jpg
P Please consider the environment before printing this e-mail
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121010/d72b77ae/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 100994 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121010/d72b77ae/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2833 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121010/d72b77ae/attachment-0005.jpeg>
More information about the Equest-users
mailing list