[Equest-users] Fw: large number of unmet hours
James Hansen
JHANSEN at ghtltd.com
Mon Oct 29 09:43:11 PDT 2012
I noticed a couple things. To use the E8 system as an example:
1) You've assigned a supply flow rate and OA flow rate at the zone of 500 CFM, yet if you let eQuest auto-size this system, it wants 1500+ CFM. So your system is undersized based on the constructions/loads you've entered in eQuest. Also, is it really 100% OA?
2) The indoor design temperatures for each zone are 120F for cooling and 40F for heating, yet your thermostat schedule is in the 60s and 70s. Make this match your real indoor design temps.
3) Your "MIN DESIGN FLOW" for a number of your zones is set to 0.00 cfm/ft2. Why?
GHT Limited
James Hansen, P.E., LEED AP
Senior Associate
1010 N. Glebe Road, Suite 200
Arlington, VA 22201-4749
703-243-1200 (office)
703-338-5754 (cell)
703-276-1376 (fax)
www.ghtltd.com
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Madjid Madjidi
Sent: Monday, October 29, 2012 12:22 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Fw: large number of unmet hours
Dear experts,
can anybody tell me why I have such a large number
of unmet hours in zone E8, E9 and E10 ? I found a lot
of advises in this user-list. Most of them are dealing the
extension of the throttling range from 2 to 4 or 6 which
only helps a little bit (especially for other zones).
Thank you in advance and with best regards
Matt
More information about the Equest-users
mailing list