[Equest-users] LEED model - constant volume terminal units

Sami, Vikram Vikram.Sami at perkinswill.com
Mon Oct 29 12:16:56 PDT 2012


1.       Sounds logical - although - why can't you specify a reheat fan system instead of a VAV system - that's probably the more appropriate system type. I'm assuming the constant volume systems are being fed by a separate AHU.

2.       If your baseline is auto sizing less than your proposed design - I would question the volume of air being designed in. Either that or maybe there is a load designed that's not being represented in the model?


Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462    f: 404.892.5823       e: vikram.sami at perkinswill.com   www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will.  Ideas + buildings that honor the broader goals of society


From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ramana Koti
Sent: Monday, October 29, 2012 1:46 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED model - constant volume terminal units

Dear All,

For a university classroom/studio building I'm modeling for LEED EAp2/c1 under the 2009 version:

The proposed design has two AHUs connected to 23 VAV terminal units and 14 Constant Volume terminal units, all with HW loop reheat from an electric boiler. The baseline system is System number 8 per Appendix G, VAV with PFP boxes, with eletric resistance reheat. The waterside of cooling is purchased chilled water in both cases.

Question 1: In the proposed design, I'm approximating the constant volume terminal units via a minimum flow ratio setting of 1.0. Is this the best way to do it?

Question 2: What is the equivalent of this in the Baseline design per Appendix G? If I repeat the same method used in the proposed design, should I let the terminal Primary CFMs default to auto-sizing? The Baseline auto-sized CFMs are lower than what is being specified in the mechanical design for the proposed model, working to my disadvantage.

Thank you,
Ramana Koti.