[Equest-users] Power induction unit/ reheat delta T
Robby Oylear
robbyoylear at gmail.com
Fri Sep 7 15:29:36 PDT 2012
ASHRAE does not mandate anything for reheat delta T in the baseline. You
can make this whatever it needs to be to meet the load, within reason of
course. Maximum recommended discharge air temperature to the zone is 15
deg F above the room temperature setpoint. Reheat delta T's of 30-40 deg F
are not unreasonable for the baseline building.
Robby Oylear, PE, LEED AP
*Mechanical Engineer*
*Senior Energy Analyst*
* *
*D* 206-788-4571
*www.rushingco.com* <http://www.rushingco.com/>
On Fri, Sep 7, 2012 at 3:05 PM, John Shen <johnshen1 at hotmail.com> wrote:
>
> I am working on a building with air handling units on each floor. Interior
> zones are served by the AHU while exterior zones are served by the AHU as
> well as FC unit which provides furthur heating and cooling. I modeled the
> system as a Power Induction Unit with series PIU to represent the FC units.
> I used a reheat delta T determined from AHU and FC's spec'd heating
> capacity and air flow rates and allowed eQUEST to autosize and distribute
> airflow. Thanks to the advice given from members on this list I was able to
> reduce my unmet hours to a reasonable range.
>
> I am working on the baseline model and am again having issues with unmet
> hours. As mentioned the heat capacity of VAV systems are determined by the
> design flow rate and the reheat delta T. In order to reduce unmet hours I
> would increase flow rates to particular zones by manually increasing Min
> design flow rates with my reheat delta T set at 20F which is what is
> required by ASHRAE. I've been at this for a while and my building is
> basically a wind tunnel, I have floors with supply cfm upwards of 100,000
> CFM and I still have thousands of unmet hours. (my throttling range are at
> 6)
>
> Am I allowed to change reheat_delta_T to a larger value?
>
> For a power induction unit with series PIU boxes, is there any way for the
> boxes to provide zone cooling? Looking at hourly reports for "zone coil
> cooling" I have 0's.
>
> Much of this might be brought about by the fact that my building heating
> and cooling load has doubled in the baseline model.
>
> Any advice would be much appreciated.
> ------------------------------
> Date: Mon, 27 Aug 2012 09:40:41 -0400
>
> From: bruce5 at bellnet.ca
> To: johnshen1 at hotmail.com
> CC: equest-users at lists.onebuilding.org
> Subject: Re: [Equest-users] Power induction unit/ reheat delta T
>
> For reference on the sim reports go to help/Tutorials and
> Reference/Detailed Simulation Reports Summary. It will explain all the
> reports. I don't use the SS-G report much. I also don't do much chilled
> water cooling. I looked at a DX design I had done and the SS-G shows no
> cooling.
> Cooling is the most difficult to get right because the delta-T is almost
> always lower than the heating side and on the heating side you can always
> cheat a little with baseboards to do a final trim even if you don't have
> them in your system. You can get a quick idea of the magnitude you are
> short. Cooling has no final trim and the eQuest focus is on cooling. You
> have also bumped into another limit on cooling capacity. You are correct
> that the cooling capacity is dependent on the delta-T and the air flow.
> There are 2 delta-T's, the one on your water and the one on your air. You
> can play with the water one all day but if you don't have enough air you
> won't get anywhere. Equest has a default on the airflow to a zone that is
> 0.6 cfm/SF. Your main AHU maximum flow will be based on this value for the
> sum of all the zones it is supplying. Most of the time this value is too
> small for a sun side perimeter zone.
> I would start with the zone with the worst unmet hours. You want to use
> zone reports, start with LS-A which will give you your peak heating and
> cooling loads for all your zones. LS-B will give you the components of
> that load except OA. SS-R is handy. Keep an eye on SV-A, it will list the
> zones and their airflow's as sub-components of the main AHU.
> You want to go to the air-side HVAC tab and select the zone you want to
> work on. Right click and select "Properties". In the "Basic
> Specifications" tab you will see on the right side half way down "Zone
> Design Flow Rates", the first value is "Min Design Flow" and is probably
> set at 0.6 cfm/SF, start increasing this value. You may need to be in the
> 1.2 cfm/SF range, it depends on the zone and the cooling load. You can
> calculate what you need too. As you bring the number up you will see the
> AHU airflow increase and also the cooling/heating capacity of the AHU
> increase in SV-A. Remember that you just want enough air. Excess air
> moving wastes energy. Your unmet hours should be decreasing for that
> zone. Some of the other zones will begin to decrease as well but your main
> problem zones should still have unmet hours. Deal with each one the same
> way.
> Remember this, it is probably THE most important setting in eQuest on the
> air side.
> Bruce Easterbrook P.Eng.
> Abode Engineering
>
> On 24/08/2012 05:16 PM, John Shen wrote:
>
> Thank you for the response, couldn't have asked for a better explanation.
>
> I was able to get the heat unmet hours down to a reasonable range.
> However, I am having difficulties with the Cool unmet hours. It appears I
> am unable to acquire any cooling capacity which is resulting in a few unmet
> hours (~150). As mentioned the heating capacity is dependent on the reheat
> delta t and airflow. I can't seem to find a place to enter delta T for
> cooling, I have coil delta T set along with an appropriate CHW loop. Yet I
> don't get any cooling in any of my zones in the SS-G section of the report.
> Any further help would be appreciated.
>
> John
>
> ------------------------------
> Date: Fri, 24 Aug 2012 09:57:49 -0400
> From: bruce5 at bellnet.ca
> To: johnshen1 at hotmail.com
> CC: equest-users at lists.onebuilding.org
> Subject: Re: [Equest-users] Power induction unit/ reheat delta T
>
> You can try changing your interior control zone as this will effect the
> base capacity that the AHU will supply to the floor. As for the exterior
> zones your heat/cool capacity is based on the delta-T and the airflow. You
> said you specified the air flow. Let eQuest auto-size the flow. By
> specifying the air flow you have removed most of eQuest's ability to adjust
> capacity. One other thing to remember is eQuest is working on the maximum
> flow as well as all the intermediate conditions as well. It is these
> intermediate loads which will trigger most of your unmet hours. As the sun
> moves across your exterior zones through the day the peak load will be
> shifting through the exterior zones as well. So a zone which was the peak
> at 10 am won't be the peak at 3 pm. eQuest will count an unmet hour if you
> are high or low on a zones temperature. By specifying the cfm to the zone
> I would guess you may be over cooling some of the zones and triggering
> unmet hours. eQuest, if allowed, would reduce the airflow to the 10 am
> zone later in the day and shift the CFM to the 3 pm zone. This is mostly
> under the hood stuff and you have to drill pretty deep into your reports to
> have an idea of what is going on and you won't find the direct answer as to
> the lower cfm to the zone. You can get an idea of the heat/cool capacity
> eQuest is dealing with in each and follow it across the building.
> Bruce Easterbrook P.Eng.
> Abode Engineering.
>
> On 23/08/2012 01:56 PM, John Shen wrote:
>
> Working on a building with an air handling unit which serves the entire
> floor. In the exterior rooms there are Fan coils to supply further heating
> and cooling to the floor. I have split the floor up into interior zones and
> exterior zones (each containing a fan coil unit). The AHU I have modeled as
> a power induction unit which serves all the zones on the floor, the
> interior zones have terminal type std VAV and the exterior zones have
> series PIU. With in the exterior zones I have specified flow rates,
> heat/cool capacity reflecting the FC. However I am getting lots of unmet
> hours from these exterior zones (~500 hrs each). I inputted a
> REHEAT-DELTA-T in of 57F (based on fan flow rates and heat capacity) into
> each of the exterior zones. This greatly reduced the unmet hours; however I
> find it strange because the unmet hours are completely dependent on
> REHEAT-DELTA-T and completely independent of the zone heat capacity. I
> appear to have a poor understanding of how the PIU system works, if anyone
> could provide further insight it would be much appreciated.
>
>
> John
>
>
> _______________________________________________
> Equest-users mailing listhttp://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> _______________________________________________
> Equest-users mailing listhttp://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120907/2cdcf713/attachment-0002.htm>
More information about the Equest-users
mailing list