Peter -
We've noticed the identical issue. Another way of stating it - the sequence of layers input for the baseline and the proposed should EXCLUDE contributions from air film. eQUEST adds the interior air film as a separate entry under the Layers tab.
[cid:image006.jpg at 01CD8F78.57E7A9E0]
ASHRAE's regulations for baseline constructions include the contribution of the exterior air film at a specified windspeed. As far as I can tell, this is how the u-value displayed on the LV-D report is calculated. (Report says "includes exterior air film").
However, we have noticed that the value displayed inside eQUEST as "calculated u-value" does not match the u-value from the LV-D. My theory is that the item shown in eQUEST includes the interior air film but not the exterior air film. (From Vol 2 dictionary, under CONSTRUCTION:U-VALUE - "For exterior surfaces, equals the overall conductance of the surface including the inside air film but excluding the outside air film.")
[cid:image008.jpg at 01CD8F78.57E7A9E0]
I'm just learning about this issue, so any wisdom from more experienced folks would be welcome!
Aaron
Aaron Dahlstrom , PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: | In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.akfgroup.com<http://www.akfgroup.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Peter Hillermann
Sent: Monday, September 10, 2012 2:02 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Building Walls
To All:
A general piece of information I got from our engineer when we had done the energy model for LEED and something to look out for. He let me know that in the baseline for wall construction to make sure you add in the air film (inside and out) otherwise LEED has an issue with your submission.
Our exact comment was this:
The Baseline Case roof and exterior wall U-values reported in Table 1.4.1A (U-0.048 and U-0.065, respectively) are
inconsistent with the U-values reported in the LV-D report (U-0.054 and U-0.063, respectively). Please ensure consistency
across construction drawings, software summaries, and the EAp2 Template.
Hope it helps.
I also don't know if anyone has this summarized, because I used the baseline walls from this forum that someone had posted and that was the response.
PS: Thank you to this forum, we ended up getting LEED Certified.
Thanks,
PETER HILLERMANN
peterh at westallarchitects.com<mailto:peterh at westallarchitects.com>
westall
architects
3404 pierce drive
chamblee, georgia 30341
o 770.458.4113
c 678.898.2936
westallarchitects.com
[cid:image001.jpg at 01CD8F76.0AC3F620][cid:image002.gif at 01CD8F76.0AC3F620]
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120910/28486421/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3221 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120910/28486421/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.gif
Type: image/gif
Size: 2436 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120910/28486421/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 23361 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120910/28486421/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 23918 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120910/28486421/attachment-0008.jpg>
More information about the Equest-users
mailing list