As an adder to this the wind speed also varies with the height of the
building. The wind speed for a locations weather file is at a standard
reference height and would also be adjusted for height of the building.
Bruce Easterbrook P.Eng.
Abode Engineering
On 12/09/2012 12:22 PM, Nick Caton wrote:
>
> I can add a probable bit of method to the madness for those concerned:
>
> The reason exterior air film is not entered as a static property, nor
> reported lumped in with the constructions' overall assembly U-values,
> is because it's actually a variable property.
>
> The reference I have handy (Table 5-12, 2001 Fundamentals) lists
> multiple resistance values for moving air (at various speeds) and
> still air (for various surface orientations and directions of heat flow).
>
> I take it as implicit that eQuest/DOE2 models this variable
> contribution from the exterior air film in consideration of the hourly
> windspeed data available from the weather file, so presenting any
> single value could be misleading. I've had to make that clarification
> a few times for those scrutinizing the construction reports without
> the eQuest detailed simulation reports reference handy ;).
>
> Hope that helps a bit!
>
> ~Nick
>
> cid:489575314 at 22072009-0ABB**
>
> **
>
> *NICK CATON, P.E.***
>
> SENIOR ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway, suite 200
>
> olathe, ks 66061
>
> direct 913.344.0036
>
> fax 913.345.0617
>
> www.smithboucher.com__
>
> *From:*equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Dahlstrom, Aaron
> *Sent:* Monday, September 10, 2012 4:20 PM
> *To:* Peter Hillermann; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Building Walls
>
> Peter --
>
> We've noticed the identical issue. Another way of stating it - the
> sequence of layers input for the baseline and the proposed should
> EXCLUDE contributions from air film. eQUEST adds the interior air film
> as a separate entry under the Layers tab.
>
> ASHRAE's regulations for baseline constructions include the
> contribution of the exterior air film at a specified windspeed. As far
> as I can tell, this is how the u-value displayed on the LV-D report is
> calculated. (Report says "includes exterior air film").
>
> However, we have noticed that the value displayed inside eQUEST as
> "calculated u-value" does not match the u-value from the LV-D. My
> theory is that the item shown in eQUEST includes the interior air film
> but not the exterior air film. (From Vol 2 dictionary, under
> CONSTRUCTION:U-VALUE - "For exterior surfaces, equals the overall
> conductance of the surface including the inside air film but excluding
> the outside air film.")
>
> I'm just learning about this issue, so any wisdom from more
> experienced folks would be welcome!
>
> Aaron
>
> *Aaron Dahlstrom , PE, LEED® AP*
>
> *In P**o**sse*-- A subsidiary of*AKF*| 1500 Walnut Street, Suite 1414,
> Philadelphia, PA 19102
>
> d: 215-282-6753| m: | In Posse: 215-282-6800| AKF: 215-735-7290
>
> e: ADahlstrom at in-posse.com <mailto:ADahlstrom at in-posse.com> | in posse
> web: www.in-posse.com <http://www.in-posse.com/> | akf web:
> www.akfgroup.com <http://www.akfgroup.com/>
>
> *From:*equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Peter Hillermann
> *Sent:* Monday, September 10, 2012 2:02 PM
> *To:* equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>
> *Subject:* [Equest-users] Building Walls
>
> To All:
>
> A general piece of information I got from our engineer when we had
> done the energy model for LEED and something to look out for. He let
> me know that in the baseline for wall construction to make sure you
> add in the air film (inside and out) otherwise LEED has an issue with
> your submission.
>
> Our exact comment was this:
>
> The Baseline Case roof and exterior wall U-values reported in Table
> 1.4.1A (U-0.048 and U-0.065, respectively) are
>
> inconsistent with the U-values reported in the LV-D report (U-0.054
> and U-0.063, respectively). Please ensure consistency
>
> across construction drawings, software summaries, and the EAp2 Template.
>
> Hope it helps.
>
> I also don't know if anyone has this summarized, because I used the
> baseline walls from this forum that someone had posted and that was
> the response.
>
> PS: Thank you to this forum, we ended up getting LEED Certified.
>
> Thanks,
>
> *PETER HILLERMANN*
>
> peterh at westallarchitects.com <mailto:peterh at westallarchitects.com>
>
> *westall*
>
> *architects*
>
> 3404 pierce drive
>
> chamblee, georgia 30341
>
> o 770.458.4113
>
> c 678.898.2936
>
> westallarchitects.com
>
> Description: Description: Description: e-signatureDescription:
> Description: Description: USGBC-Logo
>
>
> This e-mail may contain information that is confidential, privileged
> or otherwise protected from disclosure. If you are not an intended
> recipient of this e-mail, do not duplicate or redistribute it by any
> means. Please delete it and any attachments and notify the sender that
> you have received it in error. Unintended recipients are prohibited
> from taking action on the basis of information in this e-mail. E-mail
> messages may contain computer viruses or other defects, may not be
> accurately replicated on other systems, or may be intercepted, deleted
> or interfered without the knowledge of the sender or the intended
> recipient. If you are not comfortable with the risks associated with
> e-mail messages, you may decide not to use e-mail to communicate with
> In Posse.
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120912/0e973703/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120912/0e973703/attachment-0008.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 23361 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120912/0e973703/attachment-0009.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 23918 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120912/0e973703/attachment-0010.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3221 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120912/0e973703/attachment-0011.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2436 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120912/0e973703/attachment-0002.gif>
More information about the Equest-users
mailing list