[Equest-users] Can equest be used for calculating ETTV
Joe Huang
yjhuang at whiteboxtechnologies.com
Fri Sep 14 11:33:18 PDT 2012
Ery, others,
There's a deficiency in the method described in your answer because the heat flows
reported in LOADS, i.e., LS-E by space and LS-F for the whole building, are calculated at
the constant LOADS temperature, and not the actual zone (space) temperature that is
derived in SYSTEMS. This does not affect the temperature-independent heat flows (solar and
internal gains), but has a big effect on the conductive loads through the envelope,
particularly in cooling climates. About 17 years ago, Ellen Franconi (now at RMI) and I
(then at LBNL :-)) developed a method in DOE-2.1E using User Functions to take the hourly
component loads from LOADS and correct them for the true zone temperature in SYSTEMS, and
then aggregate them to produce building-level component loads. The report is available at
http://www.whiteboxtechnologies.com/download_complds_rpts.htm . Unfortunately, User
Functions have not been hooked up in DOE-2.2 yet, so this method for now can be applied
just to DOE-2.1E models.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 9/14/2012 10:46 AM, Ery Djunaedy wrote:
> My answer to the same question:
> http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2011-January/007486.html
>
>
> On 09/14/2012 11:02 AM, Nimesh Prajapati Nimesh wrote:
>> Dear Friends,
>>
>> Can equest be used for calculating ETTV ( Envelope Thermal Transfer value ) ? if yes,
>> How can we use it so that we can get this value for the building modeled.
>>
>> Thanks,
>>
>> Nimesh Prajapati
>>
>> HVAC Design Engineer
>> (+91 9687133492)
>> email: nimonomics at yahoo.in <mailto:nimonomics at yahoo.in>
>> Skype: nimonicideas
>> Please consider the environment before printing this e-mail.
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120914/f9c2fa6f/attachment-0002.htm>
More information about the Equest-users
mailing list