[Equest-users] Infra -red heating garage
Bishop, Bill
bbishop at pathfinder-ea.com
Fri Sep 14 12:01:32 PDT 2012
Assuming you are talking gas-fired infrared, you can select "Furnace" BASEBOARD-SOURCE. Efficiency, auxiliary electric (if there is a fan) etc. are input in the Unitary Power tab for the system, so you wouldn't need to document an exceptional calculation method unless you wanted to use the reduced setpoint temperature that Stormy suggests.
Regards,
Bill
[Senior Energy Engineer 28Jun2012]<mailto:wbishop at pathfinder-ea.com>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Stormy L. Shanks
Sent: Friday, September 14, 2012 2:50 PM
To: Hector Lamprea; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Infra -red heating garage
Your infrared system won't have fan power associated with it while your furnace in the baseline will have fan power. You may also be able to justify a lower space setpoint temperature in the proposed model than in the baseline since you're using radiant heat. It seems like ASHRAE has published something about what space setpoint temperatures should be used when you're designing radiant heating compared to forced air heating? Does anyone else remember that? Maybe it's in ASHRAE 55? Normally, you would have to model setpoint temperatures the same in both models.
Stormy Shanks, PE
Mechanical Engineer
www.kjww.com<http://www.kjww.com/>
From: Hector Lamprea [mailto:hector.lamprea at fundyeng.com]
Sent: Friday, September 14, 2012 1:42 PM
To: Stormy L. Shanks; equest-users at lists.onebuilding.org
Subject: RE: Infra -red heating garage
Thanks Stormy,
I guess this a good estimate, however I would like to show saving over a furnace system ( Most of the Infra-red pipes manufacturers claim between 30 to 50 % energy saving over a conventional furnace system )
Hector Lampra, P. Eng, LEED AP, CEM
From: Stormy L. Shanks [mailto:shankssl at kjww.com]<mailto:[mailto:shankssl at kjww.com]>
Sent: September-14-12 3:36 PM
To: Hector Lamprea; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: Infra -red heating garage
Hi, Hector - I recently did this for a LEED submission and had to do an exceptional calculation. There isn't a method of modeling infrared heating directly in eQUEST. I modeled it as electrical baseboard heat and assigned a sub-meter to report the kWh used by the baseboard system in the space. Once I figured out the energy usage in kWh used by the baseboard, I converted it to natural gas therms and then divided by the average efficiency of the infrared system. I submitted a narrative explaining this, and the LEED reviewer accepted the calculation method. I'm sure there are more accurate (and more time-consuming) methods for modeling it, though.
Stormy Shanks, PE
Mechanical Engineer
www.kjww.com<http://www.kjww.com/>
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org]<mailto:[mailto:equest-users-bounces at lists.onebuilding.org]> On Behalf Of Hector Lamprea
Sent: Friday, September 14, 2012 1:27 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Infra -red heating garage
Hi Guys,
Any idea how to simulate a infra-red tube heating system for a garage.
thanks
Hector Lamprea, P, Eng. LEED AP. C.E.M PO Box 6626
Intermediate Mechanical Engineer Saint John, NB E2L 4S1
www.fundyeng.com<http://www.fundyeng.com>
[Description: image001]
Serving Our Clients' Needs First Tel: 506.635.1566
Dir 506.674.9413
Cell: 506.651.5350
Fax: 506.635.0206
This communication and its attachments are confidential and may be privileged.
If you are not the intended recipient, please immediately notify the sender and then
delete this communication and its attachments without reading it or forwarding it.
Many thanks.
________________________________
This message and any attachments contain information intended for a specific party and may include sensitive or confidential material. If you are not the intended recipient, please do not read, copy, use, or disclose to others. Please notify the sender of the delivery error by reply and then permanently delete this message and all attachments.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120914/acbbf385/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 20869 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120914/acbbf385/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 2961 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120914/acbbf385/attachment-0005.jpg>
More information about the Equest-users
mailing list